Discuss Zs on lights spur of ring in the Australia area at ElectriciansForums.net
rick
At a property today I found that several lights have been taken as a spur of a ring main. At the end of the spur I get 1.33 Zs which is too high as it's on a 32A B MCB and should be lower than 1.16.
If I convert this to a fused 3A spur with FCU, can I used the 3A fuse to calculate the max Zs allowed? (which would be OK if so)
Yes that would be ok.
Reply to Zs on lights spur of ring in the Australia area at ElectriciansForums.net
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Hi, quick question. How do FCU's work? Do they just protect the load side and what I mean is, say you have a ring final with 2.5mm^2 protected by...
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...