Where does it say that an RCD or RCBO requires an additional RCD in series as a backup?
In short, it doesn't, and I don't think anyone here is saying that it does, but given the number of faulty RCDs I've come across, in my opinion, you'd be an idiot not to fit an s-type up front as back up on a TT system where the only means of providing fault protection is by way of an RCD.
I don't disagree that it's a 'good idea' to provide a backup device in the event of a faulty RCD or RCBO where these are the only means of earth fault protection.
I was just trying to get to the bottom of the assertion 'you can't use SP RCBOs on a TT supply'. So is it just the lack of discrimination with the backup RCD in the event of a neutral to earth fault or is there something more fundamental about a TT system that makes SP RCBOs unsuitable (assuming that the particular manufacturer doesn't advise against their use)?
Easiest way to look at it is page 45 OSG (green) 5.1.1 (ii)
All live conductors in a TT system and line conductors in a TN, remembering what your neutral is classed as!
The regulation that refers to is applicable to the entire installation. It isn't talking about individual circuits.
More often than not, the only effect this regulation has is forbidding the use of three pole main switches for TP TT systems.
Reply to cable behind 50mm insulated plasterboard in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I'm currently refurbishing a room and in the process adding some internal wall insulation. The wall has been stripped and my electrician has...
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...