Hi
I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single insulated mess at the moment. The right solution is a different bigger switched fuse, but there isn't room.

I don't think the standard KMF shroud could be encouraged to have a large enough cable entry without cracking/destroying it as it's designed for T&E.
There's some slack on the splitcon before it disappears up a cavity in some 25mm galv conduit with a bush on the end. It does seem that someone made an effort to comply.

Ideas/options I can imagine:
1 - get a 3 finger heat shrink boot. I've never used one but I think it's possible to use one with splitcon? Any experiences to share?
2 - there's just about room for a wiska box with a stuffing gland at top, drill 3 holes in the bottom, and mount directly above KMF. A bodge to fix a bodge, but an improvement?

I realise splitcon is not in vogue, I don't think there's a single video of someone terminating it on youtube. I only remember using it twice ever so I'm not overly familiar with it. To be clear we are talking copper stranded with multiple separate neutral and earth conductors.
Thanks for any advice.
 
Do you have a photo of the existing setup?
Some fused main switches have optional cable shrounds, wondering if one of those would fit?
 
Do you have a photo of the existing setup?
Some fused main switches have optional cable shrounds, wondering if one of those would fit?
No photo, as this customer specifically asked for no photos or videos inside her house.
It's one of these. I've used these shrouds before with T&E but I think I'd crack it trying to get splitcon with external diameter of about 16mm in, and not a lot of room to terminate too!

1713010870817.png
 

Reply to Single insulated splitcon and KMF in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

BMS installers have attended. After fitting the panel they also replaced the aged lighting in the boiler room with 6ft LED battens as instructed...
Replies
5
Views
892
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
I'm currently refurbishing a room and in the process adding some internal wall insulation. The wall has been stripped and my electrician has...
Replies
5
Views
2K
Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock