Hi Group

Had a third party inspection by a NAPIT tester, to get building control approval for a pv installation.
He has failed the cable run in Twin and Earth under my floorboards even though its greater than 50mm from surface. No 30ma RCD fitted to this circuit.

I though it was acceptable if the cable was 50mm or greater from the top of the joists?
Thanks for advice in advance

Iain
 
Did he give you a reg No that you are falling foul of?

Unless it's relevant to PV which I have no experience of, there's nothing wrong with running cables below floorboards.
Your biggest concern would be building regs.
 
Last edited:
Is it 50mm from the ceiling below too? ;) Edit - as Dave points out its not applicable anyway to running through floors.

Likewise I have no PV experience so leave that to the PV guys.
 
Last edited by a moderator:
The inverter manufacturer SMA Sunny boy guidance says do not use an RCD with a tripping current of less than 100ma to prevent false tripping which the NAPIT tester will not accept (he wants a 30ma RCD.

The cable is fully visble for all of its run from airing cupboard and along landing.

I have not asked him yet to quote the reg he's failing it on.
 
And cables below a floor Dave.

Since when? There is no requirement for cables to be RCD protected purely due to be installed under a floor, regardless of whether they are 50mm deep or not!

If you think otherwise please do quote a regulation number to back this up.
 
Since when? There is no requirement for cables to be RCD protected purely due to be installed under a floor, regardless of whether they are 50mm deep or not!

If you think otherwise please do quote a regulation number to back this up.

Dave, could you please read my post again that you've taken my quote from.

You'll see that I'm agreeing with you that cables below the floor and above ceilings do not need rcd protection.

Post 11
 
Maybe he's pulled it because you are too close to the ends of the joist thus a structural issue?

If not ask for more details and regulations that you have supposedly broken.
 
Dave, could you please read my post again that you've taken my quote from.

You'll see that I'm agreeing with you that cables below the floor and above ceilings do not need rcd protection.

Post 11

I stated that the 50mm rule only applies to walls (ie. T&E cables buried less than 50mm require RCD protection unless otherwise protected)
You replied stating that it also applies under floors

What is there to misunderstand?
 
Dave, could you please read my post again that you've taken my quote from.

You'll see that I'm agreeing with you that cables below the floor and above ceilings do not need rcd protection.

Post 11

To be honest Andy I also read your post as meaning cables below need RCD protection, at least the second part looks like that and the first part looks like you don't think it needs RCD protection!
 
I stated that the 50mm rule only applies to walls (ie. T&E cables buried less than 50mm require RCD protection unless otherwise protected)
You replied stating that it also applies under floors

What is there to misunderstand?

The misunderstanding was because I took 'Since when has running a cable under floorboards/above a ceiling required RCD protection?' To mean just that and I agreed with you.

And 'The 50mm reg is applied to cables buried in wall' to mean that cables below floors do not need to be burried >50mm and I disagreed with that.
 
As an Amazon Associate we earn from qualifying purchases.
522.6.100

Onsite Guide
7.3 Installation Considerations
7.3.1 Floors and Ceilings
Where a low voltage cable is installed under a floor or above a ceiling it must be run in such a position that it is not liable to be damaged by contract with the floor or ceiling or the fixings thereof. A cable passing through a joist or ceiling support must :

I) be at least 50mm from the top or bottom, as appropirate or...
II) have earth armouing or an earthed metal sheath, or
III) be enclosed in earthed steel conduit or trunking, or
IV) be provided with mechanical protection sufficient to prevent penetration of the cable by nails, screws and the likes (NOTE: this requirement to prevent penetration is difficult to meet), or
V) from part of a SELV or PELV Circuit
 
Last edited by a moderator:
The misunderstanding was because I took 'Since when has running a cable under floorboards/above a ceiling required RCD protection?' To mean just that and I agreed with you.

And 'The 50mm reg is applied to cables buried in wall' to mean that cables below floors do not need to be burried >50mm and I disagreed with that.

You can disagree all you like, but that doesn't make it a regulation.

Cables can be run in notches provided steel plates are fitted over the notches. Purpose made plates are available for this exact purpose.
 
As an Amazon Associate we earn from qualifying purchases.
522.6.100

Onsite Guide
7.3 Installation Considerations
7.3.1 Floors and Ceilings
Where a low voltage cable is installed under a floor or above a ceiling it must be run in such a position that it is not liable to be damaged by contract with the floor or ceiling or the fixings thereof. A cable passing through a joist or ceiling support must :

I) be at least 50mm from the top or bottom, as appropirate or...

522.6.100 does not exist

You have not included the 'or' so appear to be deliberately misrepresenting the regulation to falsely make a point.

If you are going to quote a regulation please quote the full regulation, not just part of it.
 
You can disagree all you like, but that doesn't make it a regulation.

Cables can be run in notches provided steel plates are fitted over the notches. Purpose made plates are available for this exact purpose.

You like an argument Dave,

I covered all that in post 6,

I'm just trying to help the op not show everybody how clever I am. So with that said I don't think that I can add much more to this thread and I'm getting bored with having to constantly defend myself.
 
They haven't taken it out, they've messed with the wording and remembered it.

They have to justify the ridiculous cost of a new book so they just remember a lot of regulations and adjust a few words to make the list of changes look bigger.

If you have a look at an old regs book, like the 13th edition you'll find that some regulations haven't changed at all, they just move them around and give them new numbers
 
Been in this game since 1979, and I can say never have, always drilled out timbers.

I've been in the job for 11 years and I've had notches cut in to timbers a few times.
It's always been on buildings with exposed timbers and ceilings fitted between timbers rather than below them. When you've only got an inch gap between the bottom of the floor and the top of the ceiling you don't really have much other choice. These have been new extensions to grade 1 listed buildings.
 
They don't look very thick those plates - I'm trying to remember if there was a minimum thickness requirement. Daz
 
Actually, just I've just checked reg 522.6.204 and it just states 'sufficient to prevent penetration (oo err) of the cable. Daz
 
So 522.6.100 of BS7671:2008 (2103) has moved to 522.6.201 & 522.6.204 in BS7671:2008 (2015)

Well done finding the Move DPG
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Cable run under floorboards
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
41
Unsolved
--

Advert

Thread statistics

Created
Iain123,
Last reply from
davesparks,
Replies
41
Views
15,322

Advert

Back
Top