522.6.100
Onsite Guide
7.3 Installation Considerations
7.3.1 Floors and Ceilings
Where a low voltage cable is installed under a floor or above a ceiling it must be run in such a position that it is not liable to be damaged by contract with the floor or ceiling or the fixings thereof. A cable passing through a joist or ceiling support must :
I) be at least 50mm from the top or bottom, as appropirate or...
II) have earth armouing or an earthed metal sheath, or
III) be enclosed in earthed steel conduit or trunking, or
IV) be provided with mechanical protection sufficient to prevent penetration of the cable by nails, screws and the likes (NOTE: this requirement to prevent penetration is difficult to meet), or
V) from part of a SELV or PELV Circuit
Onsite Guide
7.3 Installation Considerations
7.3.1 Floors and Ceilings
Where a low voltage cable is installed under a floor or above a ceiling it must be run in such a position that it is not liable to be damaged by contract with the floor or ceiling or the fixings thereof. A cable passing through a joist or ceiling support must :
I) be at least 50mm from the top or bottom, as appropirate or...
II) have earth armouing or an earthed metal sheath, or
III) be enclosed in earthed steel conduit or trunking, or
IV) be provided with mechanical protection sufficient to prevent penetration of the cable by nails, screws and the likes (NOTE: this requirement to prevent penetration is difficult to meet), or
V) from part of a SELV or PELV Circuit