Apologies, it should be 330W but for simplicity I wrote 300. To explain the variance i may as well describe the installation.
I have two circuits with 16A commando sockets at a building at one end of a park, there are two groups of trees. The largest of the groups has 10. Each tree is to have three 110W RGBW DMX controlled uplighters (with 100-250V PSU/Driver/DMX decoder inbuilt) fixed around the crown. Cables to be run from one to the next at a height of around 15m to enclosures to house a circuit breaker/fuse to protect each trio of fittings. This is a semi-permanent install, it will go up for around two months starting in November and then be replaced at the same time on consecutive years.
A 6mm cable could take the design current. 10mm will be too obvious, since it's quite a prestigious location I'd like to make it as discreet as possible (since they are a large land owner it's vital that this first install impresses for future business)
For my own amusement - I will not be posting the working out - could you tell me the lengths and of the cable runs:
a. DB to Commando sockets?
b. Commando socket to first tree?
c. Distance between trees?
d. CSA of cable run between DB to Commando sockets?
e. Will the lamp fittings be all turned on at the same time or in a sequence?
f. Once the lamps are on are they kept on or is some form of light show intended?
What nags in my mind is ensuring the long cable run has a sufficiently low impedance so that amalgam of all the 'top hat' current waveform of the power supplies does not create problems - such as an odd lighting effect on the observer's eye when the trees are viewed together. It would be a risk I think to do the installation without confirming not.
No promises by me to come up with a result but if I do I will post something.