S
steviethespark
Ok guys im wiring a house atm and was wondering if this set up met regulations ?i have a meter cubicle installed at the side of my garage were nie supply enters ,from there i have a set of 16mm double insulated tails feeding a set of iscos inside of garage located beside garage db ,from there i will install a 80ma time delayed trip feed from iscos using 16mm double insulated tails and 1 way incloseure ,the under ground cable i propose to use is 16mm split in 4inch sewer duct piped 30m to main house ,once entered the house will be installing 2 no 16 way hager db ,all circuits will be distributed between 4 x30ma 80a rcds with exception of smoke dection and alarm system ,the 16mm split may have to terminate into main 80a isolator and 2nd 16 way db will be fead from a 63 a mcb on same board ,hope this makes sense guys ?
what's your calculated load for the whole house, allowing for diversity? you may want to consider 25mm tails for a job that size.
hmm. just about? what if just about is not enough? have you calculated VD as well?
@ 80A i got a VD of 6.7V, so it's borderline at 80A. if your load is below 80A, fine.
just wondering what an iscos is when it's at home.
ISCO was WT Henley's original range of cast iron cutouts, service fuses and service connection boxes.
I think genuine Henley service connector blocks still have ISCO on the lids.
So basically just another name for henley blocks, Lucy blocks, mains blocks, service connector blocks etc by
I was covering the sub mains because the cable will be live from a very early stage and there will be quite a bit of digging around it for sewers ect at a later date
It's a few years since I last worked on a new build house, but when I did they always completed that kind of ground works a lot earlier in the job than the point when we started livening up the circuits. We only had the temp supply board live at that time.
And if it's being buried then split con doesn't comply as it doesn't have a complete earthed metallic layer,
U might want to check that because split does comply
check what? you want to feed a new board with a cable that has an RCD at the front of it...........
edit: just realised the quoted is on about split concentric cable lol
As far as im aware the spilt is ok to run underground via a duct something to do with the neutral and earth wrapping aroung the live conductor ,and as far as the rcd on the mains side of the submains i can drop it i was just looking little advise so cheers lads
But still underground and needing an earthed armour or similar
If the duct provides equivalent protection against mechanical damage as armour or metal sheath, then it's not required. BYB 522.8.10. I'd say that typical soil pipe probably does, although in most cases I'd use SWA anyway.
Interestingly, it doesn't seem to matter that the duct doesn't provide the earthing to a conductive tool that an earthed armour would.
Any thoughts on this question?:
What's providing the overcurrent protection to the 30m underground cable?
I wouldn't claim that the protection is the same as earthed armour, however, unless you had a considerably dense steel duct to actually prevent penetration. It is the fact that the armour is earthed which is pertinent.
As for split concentric there is a live conductor surrounding the phase conductor in places, so this couldnt really be considered to be "protecting" it.
New supply to new build
steviethespark,
Simonslimline,