A
AlarKris
I have a strange RCD tripping problem, we have a dual RCD consumer unit, when the main switch is turned off both RCD s activate, they have activated individually but not at the same time. There is no continuity between the neutrals and both sides have an insulation resistance of >25 meg, we have replaced both Rcds which are now Schneider , yet the problem still persists, everything tests fine. So I'm either missing something obvious or not, any help would be gratefully received, thanks
Any recent DIY? Somebody been fiddling with the wiring.
It would be highly unlikely for what you outline without something significant being done!
Best you compare the test results from 6 months ago with now
we have they've not altered , barely at all, and no building work has taken place, the wiring is as we left it, you can see why we are stumped, I will ask about picture locations etc....
You say with the Main Switch off both RCD's activate does the main switch not isolate the CU ?
As we turn off the main switch both RCDs trip simultaneously, it's a bugger, nothing seems to have changed and the test results are good.
The RCDs operating when the Main switch is switched off, could be due to capacitance.
Not sure if there is a solution, not sure if a solution is necessary?
As above if the RCDs trip on main switch turning off then they just need to be turned on again before you switch on again.
However saying that when you switch off the main switch the RCDs trip so you have changed the RCDs is a bit like saying I turned the kettle on and the circuit breaker tripped, I have changed the circuit breaker and the kettle turning on still trips the circuit breaker.
Have you tried a new main switch?
AlarKris,
SJD,