S
ses
Hello chaps
Got an office job where we are rewiring 3 stories with surface mounted trunking and double sockets for Computers etc
New amendment has done away with under supervision of skilled or instructed persons
The company does not have a policy in place to tell staff not to bring in their own personal items so a risk assessment will not suffice as omission of rcd protection.
Whats the best method without bankrupting me or the client to install rcd protection.
Approx 45 double sockets across 3 floors
5 for dedicated equipment servers etc
So between 12-15 sockets per floor for Computors phones etc
Two rings a floor 7 sockets on 1 rccbo
Or 3 rings a floor 3-4 sockets per rccbo
Or 40 double rcd sockets looking quite expensive
How expensive would it be for the firm to lose a full circuit of computers and possible servers - Staff down time, lost work etc I bet if it occured once it would easily cover the expense of fitting RCD sockets provided the cables themselves are not subject to rcd requirements.
Don't forget the Leakage problems associated with such an installation
Our LA spec used to be 6 doubles per circuit on a 32A RCBO for general computer use. This was seen as a maximum for earth leakage nuisance.
The dedicated use sockets for your servers etc I would definitely leave non-RCD protected if the cable route permits.
Yes servers and printers will be on non rcd sockets and circuits
Pete999 yes the earth leakage is the reason I am asking what people think is the best/halfway solution to avoid tripping
Offices that I've just completed had a free standing raised floor access system with floor box sockets. We designed it to no more than 8 computers to one circuit. 32A rcbo with 4mm hituff under the floor on tray with a separate 4mm cpc back to the board from the Last socket for high integrity earthing.
Thats not so bad then
I could split the floors into two rings with 7-8 sockets ring
Are you classing a computor as one workstation i.e computor montitor, tower and phone?
Yeah exactly that.
Servers would be best put on labelled dedicated circuits and outlets without RCD protection. 'Turned pin' 13A sockets or commando sockets could be used to prevent unauthorised use
You can get cheap and cheerful unswitched RCD sockets for about £12.
I would tend to do a risk assessment of socket use for each circuit and see if some circuits can have RCBO protection, if not then go for the RCD sockets.
All sockets are pretty much for desk use so monitor, tower phone and possibly charger
Server and printers on dedicated circuits
All cables in trunking surface mounted
Looks like rcd sockets to be safe knightsbridge or bg nexus
You only really need RCDs for the sockets that will be used for personal items.
You could label the other sockets for specified items.
The problem is that the spec is one double socket per desk
Then a surge protected extension with equipment plugged into it
Theres no policy to stop staff plugging there own items into this lead
The building is being knocked down in 4 years so the client is having a cheap and cheerful job to stop trailing leads as currently floor sockets all over the office floors