Hello chaps

Got an office job where we are rewiring 3 stories with surface mounted trunking and double sockets for Computers etc

New amendment has done away with under supervision of skilled or instructed persons

The company does not have a policy in place to tell staff not to bring in their own personal items so a risk assessment will not suffice as omission of rcd protection.

Whats the best method without bankrupting me or the client to install rcd protection.

Approx 45 double sockets across 3 floors

5 for dedicated equipment servers etc

So between 12-15 sockets per floor for Computors phones etc

Two rings a floor 7 sockets on 1 rccbo

Or 3 rings a floor 3-4 sockets per rccbo

Or 40 double rcd sockets looking quite expensive
 
How expensive would it be for the firm to lose a full circuit of computers and possible servers - Staff down time, lost work etc I bet if it occured once it would easily cover the expense of fitting RCD sockets provided the cables themselves are not subject to rcd requirements.
 
Don't forget the Leakage problems associated with such an installation
 
Our LA spec used to be 6 doubles per circuit on a 32A RCBO for general computer use. This was seen as a maximum for earth leakage nuisance.

The dedicated use sockets for your servers etc I would definitely leave non-RCD protected if the cable route permits.
 
Yes servers and printers will be on non rcd sockets and circuits

Pete999 yes the earth leakage is the reason I am asking what people think is the best/halfway solution to avoid tripping
 
Offices that I've just completed had a free standing raised floor access system with floor box sockets. We designed it to no more than 8 computers to one circuit. 32A rcbo with 4mm hituff under the floor on tray with a separate 4mm cpc back to the board from the Last socket for high integrity earthing.
 
Last edited by a moderator:
Thats not so bad then

I could split the floors into two rings with 7-8 sockets ring

Are you classing a computor as one workstation i.e computor montitor, tower and phone?
 
Thats not so bad then

I could split the floors into two rings with 7-8 sockets ring

Are you classing a computor as one workstation i.e computor montitor, tower and phone?


Yeah exactly that.
 
Servers would be best put on labelled dedicated circuits and outlets without RCD protection. 'Turned pin' 13A sockets or commando sockets could be used to prevent unauthorised use
 
You can get cheap and cheerful unswitched RCD sockets for about £12.

I would tend to do a risk assessment of socket use for each circuit and see if some circuits can have RCBO protection, if not then go for the RCD sockets.
 
All sockets are pretty much for desk use so monitor, tower phone and possibly charger

Server and printers on dedicated circuits

All cables in trunking surface mounted

Looks like rcd sockets to be safe knightsbridge or bg nexus
 
You only really need RCDs for the sockets that will be used for personal items.
You could label the other sockets for specified items.
 
The problem is that the spec is one double socket per desk
Then a surge protected extension with equipment plugged into it

Theres no policy to stop staff plugging there own items into this lead
 
The building is being knocked down in 4 years so the client is having a cheap and cheerful job to stop trailing leads as currently floor sockets all over the office floors
 