So what do they do when they have a power failure !
The servers will be just fine.
Just divide circuits up.
If they wanted a 24/7 uptime system then he will have to spend lots of money.
I don't see why you are trying to go out of your way to omit the RCD?
Why do you think that plugging in a server the RCD will suddenly become unstable and keep tripping!
When was the last time your computer at home operated your RCD? im willing to bet never unless it has a fault.
The server will be feed from a socket, and that socket will need RCD.
Whats the big difference Dave? Server goes off, server gets put back on when power is restored !
Where is this big nuisance problem coming from?
There's not Spin, but my point was regarding plugging a server into a general socket with RCD protection.
There seems to be a switch in people's heads that as soon as the word "server" is mentioned they run around like headless chickens and the world as we know it will end.
not my regs with me (in hospital) but there are a design for rings and radials,where leakage is an issue, sorry I can't point you in the right direction but it's in there somewhereYes servers and printers will be on non rcd sockets and circuits
Pete999 yes the earth leakage is the reason I am asking what people think is the best/halfway solution to avoid tripping
Not aware that there has been a change in the requirements which now require sockets intended for a specific item of equipment to be provided with RCD protection?
Perhaps someone can quote the Regulation which now requires all sockets to be provided with RCD protection?
I did have a look but couldnt see anything other than circuits should be designed to limit tripping on rcds and about high earth leakage having dual earth path
I remember reading that equipment that is designed to be on a plug top the maximum permitted earth leakage is 3.5mA. Any equipment that produces more than 3.5mA should be hard wired. Ill try find it.
543.7.1.201 Equipment having a protective conductor current exceeding 3.5 mA but not exceeding 10 mA, shall
be either permanently connected to the fixed wiring of the installation without the use of a plug and socket-outlet or
connected by means of a plug and socket-outlet complying with BS EN 60309-2.