Just a thought.
Is it possible that the other 2 light fittings are faulty and back feeding down the neutral?
I would of thought any faults to cause this at these 2 fittings would be enough to trip the mcb or rcd.
I've been thinking again and still puzzled to how all the fittings come on when they have independent switches and the switch lives work as they should with the circuit off!![]()
Don't make it complicated! IR tests as suggested, plus take down the fittings and inspect/test the terminals, whilst the fittings are down put 2 normal pendant lights up to see if it still trips or if it now works. Plus draw out a diagram of the switches and lights to make sure all conductors are where they should be.