Just a thought.

Is it possible that the other 2 light fittings are faulty and back feeding down the neutral?

I would of thought any faults to cause this at these 2 fittings would be enough to trip the mcb or rcd.

I've been thinking again and still puzzled to how all the fittings come on when they have independent switches and the switch lives work as they should with the circuit off! :hammer:

Don't make it complicated! IR tests as suggested, plus take down the fittings and inspect/test the terminals, whilst the fittings are down put 2 normal pendant lights up to see if it still trips or if it now works. Plus draw out a diagram of the switches and lights to make sure all conductors are where they should be.
 
Last edited:
Don't make it complicated! IR tests as suggested, plus take down the fittings and inspect/test the terminals, whilst the fittings are down put 2 normal pendant lights up to see if it still trips or if it now works. Plus draw out a diagram of the switches and lights to make sure all conductors are where they should be.

Yeah I have been over thinking I think.

I have some pendants ready to put in later as well as a Meggar.

Fresh head today so hopefully go smooth.
 
Don't make it complicated! IR tests as suggested, plus take down the fittings and inspect/test the terminals, whilst the fittings are down put 2 normal pendant lights up to see if it still trips or if it now works. Plus draw out a diagram of the switches and lights to make sure all conductors are where they should be.

I would take them down first!
 
ither switch seemed to give a supply all 4 lights even though the switch wires cannot be connected as they are on separate twin and earth's from switch
still puzzled to how all the fittings come on
Do lamps actually light amongst both groups or do you simply mean you read a voltage? If the lamps light, but a continuity test between the two switched lives gives no reading, either the fittings have somehow got wired in some bizarre series arrangement and could never have worked properly, or a fault between the two SL's (e.g. screw through cables) is breaking down at mains voltage but tested clear to your multimeter. (I expect your original IR tests didn't include between the SLs). In any case if it was that marginal, I'd expect it to flicker and the fault to burn itself out eventually,
If you just meant there was a voltage measured at the 'switched-off' group, then capacitive coupling between the cables where they run together down the switch drop is the likely (harmless) cause. If the IR between them tests OK (SL of group 1 to SL of group 2) it wouldn't surprise or concern me. An approved voltage indicator would not have given the misleading reading.

One thing I noticed when mcb off, I had 0.8v DC between the 2 switch lives at switch??

Perfectly normal, there are capacitors inside the LED lights can store some residual DC charge which can leak back to the terminals while off.
 
Do lamps actually light amongst both groups or do you simply mean you read a voltage? If the lamps light, but a continuity test between the two switched lives gives no reading, either the fittings have somehow got wired in some bizarre series arrangement and could never have worked properly, or a fault between the two SL's (e.g. screw through cables) is breaking down at mains voltage but tested clear to your multimeter. (I expect your original IR tests didn't include between the SLs). In any case if it was that marginal, I'd expect it to flicker and the fault to burn itself out eventually,
If you just meant there was a voltage measured at the 'switched-off' group, then capacitive coupling between the cables where they run together down the switch drop is the likely (harmless) cause. If the IR between them tests OK (SL of group 1 to SL of group 2) it wouldn't surprise or concern me. An approved voltage indicator would not have given the misleading reading.



Perfectly normal, there are capacitors inside the LED lights can store some residual DC charge which can leak back to the terminals while off.


Thanks for the reply.

With mcb off:

- No continuity through SL1 and SL2 (just 0.8v DC)
- SL 1 operates 2 lights only and SL2 operates 2 other lights only (how it should work)

With mcb on and either switch on:

- Voltage at all lights
- all lights come on but within a few minutes mcb trips again

This is with 1 light on each set connected.

Very bizarre (technically possible) if there is a fault between SL's as no work has been carried out and they are in separates twin and earth's.

Will be IR testing tonight so hopefully find the answer.
 
Last edited by a moderator:
ever thought it could be a faulty MCB? if lamps have been blowing, the MCB could have been damaged by surges.
 
pay my air fare to cornwall and an overnight stay in a nice pub and i'll come down and sort it for you. :35:
 