Pauldicker

Dear all

I have been called out to a customer today as they have been experiencing tripping issues. However sometimes its one rcd then a while later it may be the other and sometimes its both at the same time.

I have looked at appliances, e.t.c however they do not cross both circuits. The customer said its happened over the last few months. They have experienced regular power cuts so i did wonder if a power surge could be the issue.


Any ideas?
 
But what would explain them tripping individally or both together. This is also when under no load
 
But what would explain them tripping individally or both together. This is also when under no load


Err..... A fault or faults.

Just this week I traced a "no load" fault to cables behind a socket where the earth was touching the live

Does it happen more frequently during wet weather?
 
But what would explain them tripping individually or both together. This is also when under no load

RCDs trip either because they are faulty or because they are detecting an imbalance.
They may not have any apparent load on them but may have a fault current through them.

Trying to guess why at this stage is impossible, work that out afterwards.

It wouldn't be out of the question after the fault is found, possibly to be an alteration or meddling, for the customer to admit to such.
 
They noticed it more this tuesday with the rain. However there were a few power cuts in the road. I could not find any obvious water ingress
 
Any extrnal electrics, you mentioned it tripped after a rainy day?
 
Have you done any IR tests? That's the first thing I'd do. Leave everything plugged in and test LN-E. NOT L-N!
I can recall only a handful of RCD tripping issues I haven't quickly traced by IR testing.
 
Last edited by a moderator:
I havent done an ir test yet i wanted to narrow it down before i start charging. Its been happening on and off for a couple of months. But as i described it could be either of the rcd's or both at the same time.
 
A few years back I went out to a property that had a "nuisance" tripping problem. It turned out to be a "faulty" extension lead. In fact it was a four gang short extension that the owner of the property later admitted he had changed the plug on a while back. He had mistakenly connected the earth and neutral wires the wrong way round. All that was ever plugged in was his alarm clock and the RCD only tripped occasionally.

My point being that part of your investigation into finding the fault may include quizzing the property owners. They may not realize the significance of something so simple, much like my example above.
 
I havent done an ir test yet i wanted to narrow it down before i start charging. Its been happening on and off for a couple of months. But as i described it could be either of the rcd's or both at the same time.
I am a bit puzzled by this, what are you charging?? MFT batteries? Customer? Braincells?? in like a bull?
 