Piratepete

Hi Guys
No doubt this has been asked before, and the answer is already out there somewhere but I'm tired and the job is tomorrow so please bear with me.

Existing CU is back entry, spaced off the wall by an inch on a couple of vertical battens in a tight wooden cupboard. I'm intending the same mounting and cable entry arrangement

Back entry requirement is IP2XC which allows a gap of about 12mm od at each gland. It occurs to me that having gaps like this doesn't help if you're trying to keep an internal fire contained.

Is there any requirement to fill any gap between the cables and the edge of the quite large entry holes?

Cheers

Pete
 
I'm confuse. IP rating for enclosure, CU is top and sides. As wirepuller is saying, nothing required for back of CU. But if its in a wall unit, isn't there a back panel (wall unit) as well?
 
I'm confuse. IP rating for enclosure, CU is top and sides. As wirepuller is saying, nothing required for back of CU. But if its in a wall unit, isn't there a back panel (wall unit) as well?
There wouldn't be a requirement for back entry because the board should be flat to the wall. No idea why people mount them upon battens.
 
There wouldn't be a requirement for back entry because the board should be flat to the wall. No idea why people mount them upon battens.

If you have cables run on the surface from above, it's much easier to route them in through a good sized (non-accessible) hole in the rear than get an IP4X entry on the top face. Also easier when adding cables later, as there's no need to be cutting extra holes in the enclosure, which can be difficult if access is restricted.
 
If you have cables run on the surface from above, it's much easier to route them in through a good sized (non-accessible) hole in the rear than get an IP4X entry on the top face. Also easier when adding cables later, as there's no need to be cutting extra holes in the enclosure, which can be difficult if access is restricted.
Contain them in trunking.
 
I agree Handysparks. Some times its not an option to use trunking due to cables being painted over and decoration etc. personally though I would prefer to use a CU patress.
 
If you have cables run on the surface from above, it's much easier to route them in through a good sized (non-accessible) hole in the rear than get an IP4X entry on the top face. Also easier when adding cables later, as there's no need to be cutting extra holes in the enclosure, which can be difficult if access is restricted.
What is a non accessible hole, and if it is how does this aid future cable entries?
 
If you can't reach the edges of the hole with a finger then, in my opinion, it's safe. Of course, you can still manoeuvre a new cable into the enclosure.
Each to their own, the only time I could maybe understand battens was if the surface was uneven. Different people different standards.
 
If in a cupboard and not worried about aesthetics I would get rid of the battens and go straight into the top of the unit with stuffing glands, if worried about what it looks like then contain all in square conduit butted to top of board. Personally I don't like battens with holes down the back. If the wall/plasterboard was shot/wonky or holes too big I would back with a ply mounting board.
Oh and the answer to your actual question is no!:-)
 