Currently reading:
Full rcbo boards????
Discuss Full rcbo boards???? in the UK Electrical Forum area at ElectriciansForums.net
D00DY_T00DY
Hi all,
Probably going to seem like a novice question just wondering what techniques you lot have for full rcbo boards to keep it neat.
Put 5 in today for a temporary supply for ground workers on a genny; earth rod with a Zs of 2.13ohms (fairly good?)
Anyway it was a complete nightmare trying to keep it neat with the earth and neutral flexes out of them.
I've only installed less than 10 just wondering all your techniques for rcbos?
I kept all the length on these and tried to coil them nicely behind the cpc and neutral terminals.
I cable tie them and loop them behind incoming L-N and splay them up to the terminal. Was thinking of ferruling them with shorter cable. The functional earths are crazy though at what .5mm? and also long, it is a bit messy and annoying I have to work with such tat.
Some say there isn't actually a conducter In there at all :D
I tried connecting all the rcbo flexes out then get them all together then connect my circuits but fighting 6mm wires round was just a pain so I'm thinking circuits first then move the flex round the circuit wires and cable tie them all together.
It'll be a while till I'm installed rcbos again though.
I agree, I did an 8 way Wylex the other day and was doing great with neatness which all went to pot with the functionals and the neutrals. I cable tied across in a group of 2 then splayed.
Good experience though. Was a small dimension board though as it had to fit in a meter box!
Well indeed a spark I know just connects even the functional earth to neutral. It does get me though as the FE is so small and mixing sizes in the same termination is somewhat unreliable.
Hi all,
Stick some functional earth coloured sleeving over them cut to length, nice and neat no problems imo
Cut and ferrule for me every time.
Like to leave a little bit length still so the RCBO isn't completely useless if it does need to be moved a little in the future.
I beg to differ. RCBOs are far better than the dual RCD boards with massive tails cluttering up the whole space. I just cut the neutral lead down to size and fit a 4 or 6mm2 boot lace ferrule. These things cost pence. As for the f/earth , take them to below the bus bar, into a wago 222 then take a 2.5mm2 single from wago222 up to earth bar. Also if you are installing C/U as a replacement there is much less chance of nusance tripping.
very neat, mate.
Was done last year for my CPS assessment, looking at it now (a year down the line) and I'd argue there's room for improvement. I think if I'd done it today I'd have learnt a few more tricks and it would be neater still.
Thought I had some photos of a Proteus (absolute s****) 3-phase board I done recently where I'd cut and ferruled but I've checked and seems I didn't bother to get the camera out.
I know the kqi Schneider rcbo instructions tell you not to bundle the neutrals together but can cut to length.
They recommend if the functional earth is cut then a bootlace is fitted due to crushing of the fine strands when tightend in the terminals
Rcbo tails should be cut to length and not bundled up in the board as this can lead to overheating of the conductor. Some, such as Schneider, even have this detailed in the instructions.
I'm curious about the Zs quoted in the OP, any Zs measurement on a generator fed installation won't include the earth rod, it will be testing the return path directly to the star point of the alternator.
The Ra for generator earth rods has to be measured using an earth electrode testing method.
Temporary supply mate, might be in a month max. Probably try blag the company to give him the cable and gear back since they won't use it :D did on the last tempory supply we did haha
Boss does the testing, I took a Zs at the board after I finished. That's what I was referencing
Does your boss not include you in the testing process? Did you see him set up temporary electrodes and test the earth rod at any point in time?
Your Zs measurement almost certainly did not include the earth rod. You will have been testing via the cpc straight back to the star point via the N-E link at the generator
With a generator fed installation the earth electrode is the earth reference of your TNS system. In comparison to a normal installation the generator is equivalent to the substation transformer.
Reply to Full rcbo boards???? in the UK Electrical Forum area at ElectriciansForums.net