H

hightower

I've got a couple of smokes to fit in a separate building at the school. The building is known as the Caretaker's House, it's the old caretaker's living quarters but not used for that purpose (and hasn't for decades). It's going to become the school's behaviour centre - basically somewhere to send the naughty kids where they can still get an education but not interfere with the good kids. Seeking advice from those higher up in the council, they have said that it needn't be linked to our part 1 alarm system, and can instead be covered by a couple optical smokes - this is because the building is completely separate to that of the school, physically.

So with that in mind, what certification would you fill out? I was thinking part 6 with it being a house, but then I realised it's still a commercial premises.

Any advice on this one?
 
I agree with all above.
How will a remote building covered by only smoke detectors alert a fire in that building to the main monitored panel.
I think someone is too concerned with the balance sheets .
 
I have worked in lots of schools and have never seen a Part 6 system even in the smallest of buildings. You also have to consider the escape route from this building, do they have to enter the main building as part of this route in which case the systems would require linking. Generally separate buildings on educational premises will be linked.
 
If people are implying I'm cutting costs, I can assure you that I have an email direct from the Senior H&S (Fire) Advisor stating, and I quote:

"As per our earlier conversation . I can confirm that the house does not need to be linked to the schools fire detection system.

However I would advise that you have a hard wired smoke detector installed in the hall and upstairs landing to give early warning of fire to any occupants who may be on the first floor. "

I guess this is a discussion on it's own, but that's not what I'm asking. I'm just wondering what cert should I use to cover one's backside.
 
If people are implying I'm cutting costs,
I can assure you that I have an email direct from the Senior H&S (Fire) Advisor stating, and I quote:

"As per our earlier conversation . I can confirm that the house does not need to be linked to the schools fire detection system.

However I would advise that you have a hard wired smoke detector installed in the hall and upstairs landing to give early warning of fire to any occupants who may be on the first floor. "

I guess this is a discussion on it's own, but that's not what I'm asking. I'm just wondering what cert should I use to cover one's backside.

No not you - They .
I would never doubt your integrity.

Covering you backside would always be using the highest standards available.
 
No not you - They .
I would never doubt your integrity.

Covering you backside would always be using the highest standards available.

I agree, but when the bursar has an email saying £100 of smokes will suffice compared to getting an extension to our main system, they are going to pick that option all day long. They've got an email covering their backsides, so now I need to cover mine with the correct certification.
 
Are they assuming it is still a dwelling HT.
No, they know the intended purpose of the building. It has a boiler in the kitchen still and I asked whether it would be prudent to fit a CO - his response was no since nobody will be sleeping in the premises.
 
What am I to do though but install the system they have said is sufficient and sign it off as best as possible.
 