Page 134 of Part 1 states a Typical Category of system for Schools would be M or M/P2 or M/P2/L4 or M/P2/L5 - surely smokes installed in this way is a P2 as Andy has said.

Your smoke alarms (i assume Aico type) would need to satisfy the recommendations from page 22 BS 5839-1.
I'm not 100% sure but I dont think they carry any of the listed BS numbers required.
 
Weather BS5839 Pt 1 2013 is cover or not, the ball is in the clients hands. They need to carry out the risk assessment, and have stated what is required. This is why the variation section is used frequently on Fire certs to state the obvious. You can only advise and request the senior officer signs the design cert....after all it`s his head on the line, not yours, you have been told to carry out the work to his design.
 
If people are implying I'm cutting costs, I can assure you that I have an email direct from the Senior H&S (Fire) Advisor stating, and I quote:

"As per our earlier conversation . I can confirm that the house does not need to be linked to the schools fire detection system.

However I would advise that you have a hard wired smoke detector installed in the hall and upstairs landing to give early warning of fire to any occupants who may be on the first floor. "

There is no mention of BS5839 part 6 just that the smoke detectors must be hard wired which could refer to a stand alone part 1 system. I think the Senior H&S (Fire) Advisor needs to clarify his statement rather than pass the role of decision making to someone else based on his half cocked less than clear email

I guess this is a discussion on it's own, but that's not what I'm asking. I'm just wondering what cert should I use to cover one's backside.

Don't know how big your backside is but an A3 sized cert might be a good start. Without any clear design criteria you are installing something that you are unsure of its suitability for which no certificate will cover your derriere
This is where H&S falls over there are too many people assessing things when they have little or no knowledge of what they are assessing

I agree, but when the bursar has an email saying £100 of smokes will suffice compared to getting an extension to our main system, they are going to pick that option all day long. They've got an email covering their backsides, so now I need to cover mine with the correct certification.

For a part 1 system the smokes could cost £100 if you ignore all the associated equipment needed for a part 1 system
Even a part 6 installation is going to cost more than £100 by the time you install the interlinking cable so I suspect someone is speaking out of turn here without understanding what is actually required

I would suggest that whatever system is installed it needs to have sounders similar to the existing school system to avoid confusion if there is ever a fire
 
I'm really not sure what to do. I've already installed the hard-wired interlinked Part 6 smokes, but I think I'm just going to send an email to the bursar to explain that I really don't think it's sufficient and to strongly consider either fitting a standalone part 1 system, or an extension to our current system.

I was speaking to my Dad and brother over the weekend (they both work for the Council too). It went something like:

Me: Do you know Joe Bloggs?
Dad/Brother: Yes
Me: What do you think of him?
Brother: Meh, he's alright, played football with him yesterday.
Me: No, I mean how is he at his job. (I then explain about this situation)
Dad: (Dad deals with CCTV and door automation stuff) Well I was doing a site walkaround with him for some emergency doors, (he was looking at putting a new magnetic system in place - the current mags are broken or something, I forget the particulars), the occupier was asking what to do for security of the doors with the mags being faulty, and Joe said "stick a bolt in it". I said "it's a means of escape, you can't do that" to which his response was something like "it's fine, it's a temporary measure, we'll do a risk assessment for it."

Keith Lard is coming to my mind now, but I'm super worried about my situation. All I can think of is to send the email and see what comes. Anyone got any further ammunition for me to put in the email and make sure it packs a punch?
 
Hi HT - yes, send an email by all means. But perhaps keep your note very short - asking him to please clarify the design of the proposed fire safety system. He will either do that, or say you do it. Either of which will lead to further discussion. :)
 
Hi HT - yes, send an email by all means. But perhaps keep your note very short - asking him to please clarify the design of the proposed fire safety system. He will either do that, or say you do it. Either of which will lead to further discussion. :)

He's the type of person who is very hard to get hold of, it took a lot of effort to get him to put in to writing his 'design' as it is.

I think I'll be emailing my boss rather than this guy directly, then it's up to her if she wants to take it any further. Although I will definitely be mentioning (verbally) my Dad's story too. I just don't like the whole scenario in the slightest.

Has anyone ever visited this site or risk assessed it.

Yes, this H&S guy has had a walkaround when we said we were re-purposing it.
 
I feel that you have been placed in the firing line, but I also feel that you can automatically dodge the bullet since you are installing the protection requested by a (presumed!) competent senior person. The extent of your responsibility is to ensure that the system installed works correctly, whether it is fit for purpose is not your responsibility.
Presumably, even though I am not sure I agree with it, the intent is that there will be only supervised and alert people in the building at any time and the smoke alarms provide warning of a fire to allow evacuation of the building if the fire occurs in an inobvious location and if the building is empty then a fire in this building will not imperil the rest of the school therefore interlinking with the main system is not required.
This seems to me to be an inappropriate design, but some rationale can be provided.
If you complete the paperwork without a design section and with variations and source of design data as Tazz has suggested and indicate where it does not meet the desired specification from BS5389 then you have done as requested.
Providing a written advisory to the school authorities to indicate your belief that this system is not capable of providing a similar level of protection as there is in the rest of the school and does not meet with the recommendations from BS5839 pt1 would be a useful exercise to protect yourself but need not be overly detailed, just clear cut and non confrontational.
If you have done this then there should be no problem or worry at your end.
I hope you can resolve this to a level with which you are happy.
 
So is the certification need just H.2 of 5839-1? Installation certificate? Or should I also complete H.3 for commissioning. What about H.4, should I get somebody (like my boss) to complete an acceptance certificate?
 
Okay, so I'm completing some documentation if people can help.

First up I have created a document with my objections as follows:

Having been tasked with installing a fire detection system to the Caretaker’s House based on the specification provided by NAME REMOVED (Senior Health & Safety (Fire) Advisor), I am writing this to document my objections and recommendations.

The system specified by NAME REMOVED (attached) is a Grade D LD3 system conforming to BS5839 Pt 6 – a standard designed to be applied to domestic premises. The Caretaker’s House is not currently used as a domestic premises, instead housing staff and students throughout the school day, and it is therefore my strong recommendation that a fire detection system to BS5839 Pt 1 is appropriately designed and installed.

Having completed the requested works, I have completed an installation certificate (attached) based on the specification provided by NAME REMOVED which details the type of system installed and the source of this design, but I would recommend at the very least that a design certificate for the system is requested from NAME REMOVED.

As well as that, I've printed his original emails and attached them to the document. Furthermore, I've completed the H.2 Installation Certificate from BS5839-1, with the following details:

Extent of installation work covered by this certificate: Installation of two Aico BS5839-6 smoke alarms, hard-wired with battery backup and hard-wired interlink - one in hallway, one on upstairs landing.

Specification against which system was installed: See attached email from Senior Health and Safety (Fire) Advisor, NAME REMOVED.

Variations from the specification: Part 6 system installed as specified in the design, to Grade D LD3. As the installer, I have separately documented my objections to this design.

-----

Does this look okay, and have I covered everything? Would you change and/or add anything?

Thanks everyone, appreciate you all seeing this one out with me.
 
Rather than objections I would use the term Non Compliant with the current British and EN Standards

As previously mentioned by someone it is a new system in commercial premises that now has the additional requirements of VAD's to be installed. There is no place for a BS5839 pt6 in this building and the H&S man should know this and if he doesn't he should know his limitations or get the appropriate training or resign the day job

I'm not sure I would put my name on anything that would associate me with this installation, your problem is your lack of specialist knowledge of fire alarm requirements has led you into this trap and all to quickly the nameless H&S man will feed you to the wolves if something goes wrong, it's a management book passing trait that goes on across many industries
 
Rather than objections I would use the term Non Compliant with the current British and EN Standards

As previously mentioned by someone it is a new system in commercial premises that now has the additional requirements of VAD's to be installed. There is no place for a BS5839 pt6 in this building and the H&S man should know this and if he doesn't he should know his limitations or get the appropriate training or resign the day job

I'm not sure I would put my name on anything that would associate me with this installation, your problem is your lack of specialist knowledge of fire alarm requirements has led you into this trap and all to quickly the nameless H&S man will feed you to the wolves if something goes wrong, it's a management book passing trait that goes on across many industries

Thanks, I've amended below. As for putting my name to it, I feel that is better (with the relevant highlights showing my objections) than to turn a blind eye to it all. I've installed the smokes now and need this in place to cover me (and ultimately force the school to do something more appropriate). Any more comments before I send to my boss?

----


Having been tasked with installing a fire detection system to the Caretaker’s House based on the specification provided by NAME REMOVED (Senior Health & Safety (Fire) Advisor), I am writing this to highlight my concerns and recommendations.

The system specified by NAME REMOVED (attached) is a Grade D LD3 system conforming to BS5839 Pt 6 – a standard designed to be applied to domestic premises. The Caretaker’s House is not currently used as domestic premises, instead housing staff and students throughout the school day, and it is therefore my recommendation that a fire detection system to BS5839 Pt 1 is appropriately designed and installed.

However, having completed the requested installation, I have also completed an installation certificate (attached) based on the specification provided by NAME REMOVED which details the type of system installed and the source of this design, but I would recommend at the very least that a design certificate for the system is requested from NAME REMOVED.

To summarise: at current, I fear the install is non-compliant with the current British and EN Standards which apply that only a correctly designed and installed system to BS5839 Pt 1 can achieve.
 
Seems to cover most things as best you can.
You have not signed to accept design of the system installed, though you should complete commissioning (assuming you have commissioned it)
It is fine but I might reword the last paragraph if I was writing it.
To summarise, at present I believe that the installation does not comply with current British and UN standards as this can only be achieved by the installation of a system designed correctly to BS5839-1:2013.
 