Okay, so I'm completing some documentation if people can help.
First up I have created a document with my objections as follows:
Having been tasked with installing a fire detection system to the Caretaker’s House based on the specification provided by NAME REMOVED (Senior Health & Safety (Fire) Advisor), I am writing this to document my objections and recommendations.
The system specified by NAME REMOVED (attached) is a Grade D LD3 system conforming to BS5839 Pt 6 – a standard designed to be applied to domestic premises. The Caretaker’s House is not currently used as a domestic premises, instead housing staff and students throughout the school day, and it is therefore my strong recommendation that a fire detection system to BS5839 Pt 1 is appropriately designed and installed.
Having completed the requested works, I have completed an installation certificate (attached) based on the specification provided by NAME REMOVED which details the type of system installed and the source of this design, but I would recommend at the very least that a design certificate for the system is requested from NAME REMOVED.
As well as that, I've printed his original emails and attached them to the document. Furthermore, I've completed the H.2 Installation Certificate from BS5839-1, with the following details:
Extent of installation work covered by this certificate: Installation of two Aico BS5839-6 smoke alarms, hard-wired with battery backup and hard-wired interlink - one in hallway, one on upstairs landing.
Specification against which system was installed: See attached email from Senior Health and Safety (Fire) Advisor, NAME REMOVED.
Variations from the specification: Part 6 system installed as specified in the design, to Grade D LD3. As the installer, I have separately documented my objections to this design.
-----
Does this look okay, and have I covered everything? Would you change and/or add anything?
Thanks everyone, appreciate you all seeing this one out with me.