I have seen many EICR/PIR's that are worthless carried out by letterbox "bent towards Observation" electricians with a "Lim" overuse condition especially in L/N-E IR testing, it does not help anyone down the road especially fault installation history. I accept L-N is not always clear due to something somewhere attached but I still try to whittle that down and note the result. So faced with a large number of 12v downlights I presume you drop them all with the associated damage to the ceiling and disconnect the transformers so you can do a L-N IR test?
A global LN-E test on a domestic CU which gives a satisfactory reading will confirm that each and every final circuit is satisfactory. If the global is not satisfactory THEN start breaking it down.
If only people or organisations were educated to realise the importance of electrical testing and how involved it is. Then we may get the recognition and time it deserves.
I now challenge/question any silly recent reports I come across....it just gives this trade a bad name.