I did one this week - the IR on one bank of circuits came back as almost zero N - earth.

I then did individual tests om each of the 4 circuits to ifentify the one with the issue. Still a C2 but at least there is only 1 to investigate is they want it fixed!
 
I did one this week - the IR on one bank of circuits came back as almost zero N - earth.

I then did individual tests om each of the 4 circuits to ifentify the one with the issue. Still a C2 but at least there is only 1 to investigate is they want it fixed!
Cooker circuit?
 
I would say that you should be verifying a particular circuit has an earth rather than getting a test meter and potentially whacking 25 amps worth of test current down the circuit.
Exposed parts /pipework that aren’t earthed can become a shock risk.

However I do realise that most test instruments won’t allow the test if the touch voltage detected is greater than 50 v
 
I would say that you should be verifying a particular circuit has an earth rather than getting a test meter and potentially whacking 25 amps worth of test current down the circuit.
Exposed parts /pipework that aren’t earthed can become a shock risk.

However I do realise that most test instruments won’t allow the test if the touch voltage detected is greater than 50 v
If there is no earth there will have been a shock risk long before you turn up to test.
 
If there is no earth there will have been a shock risk long before you turn up to test.
Maybe , just highlighting the fact that if you’re test instrument doesn’t have the touch voltage safety feature then you will potentially make a bad situation worse.

Not really sure if them type of test instruments exist/ are used?
 
Keep a record of the person who did the EICR. Tell the customer. - Not that you can do anything with it mind you.
Perhaps making it public on these forums that they are being noted might make some pull their socks up. I have about four in this category. More or less blank ( or completely wrong) EICR. Satisfies many landlords though.
A domestic EICR on an old house is an exhausting full-on day. I'd often be still writing it up at 11pm or next day.
I do work for some housing agencies that expect you to churn out as many EICRs in a day as possible.. telling them that the guys they have must be skipping over details or not testing things at all they just say "well its passed all the relevant tests" I just laughed... it takes me a good day to do a thorough test
 
Last edited by a moderator:
Zs won’t show show broken rings , or whether a neutral is lose in a socket/jb etc.

If I get paid for a full test I do the lot, except pull downlight down or take fancy light fittings down ( unless I suspect a fault there )

Customer get an all clear with a full set of new results to replace the missing ones.
 
I have seen many EICR/PIR's that are worthless carried out by letterbox "bent towards Observation" electricians with a "Lim" overuse condition especially in L/N-E IR testing, it does not help anyone down the road especially fault installation history. I accept L-N is not always clear due to something somewhere attached but I still try to whittle that down and note the result.
If only people or organisations were educated to realise the importance of electrical testing and how involved it is. Then we may get the recognition and time it deserves.
I now challenge/question any silly recent reports I come across....it just gives this trade a bad name.
 
Zs won’t show show broken rings , or whether a neutral is lose in a socket/jb etc. Neither will an R1+R2 which was the only test I suggested may be superfluous.

If I get paid for a full test I do the lot, except pull downlight down or take fancy light fittings down ( unless I suspect a fault there )

Customer get an all clear with a full set of new results to replace the missing ones.

I have seen many EICR/PIR's that are worthless carried out by letterbox "bent towards Observation" electricians with a "Lim" overuse condition especially in L/N-E IR testing, it does not help anyone down the road especially fault installation history. I accept L-N is not always clear due to something somewhere attached but I still try to whittle that down and note the result. So faced with a large number of 12v downlights I presume you drop them all with the associated damage to the ceiling and disconnect the transformers so you can do a L-N IR test?
A global LN-E test on a domestic CU which gives a satisfactory reading will confirm that each and every final circuit is satisfactory. If the global is not satisfactory THEN start breaking it down.

If only people or organisations were educated to realise the importance of electrical testing and how involved it is. Then we may get the recognition and time it deserves.
I now challenge/question any silly recent reports I come across....it just gives this trade a bad name.
 