Evening all, just a quick question from a non electrician before you shout! Our systems are all installed using a sub DBB (rather than into the existing board). Normally we would fit using 25mm tails however a contract we are currently on say that 10mm tails can be used............any views?
 
We need a lot of information before we can advise.
What is the nature of the installation? Commercial/domestic
What is the design current here?
What and where is the overload and fault protection relevant to these tails?
What is the installation method for the tails?
 
We need a lot of information before we can advise.
What is the nature of the installation? Commercial/domestic
What is the design current here?
What and where is the overload and fault protection relevant to these tails?
What is the installation method for the tails?

These are domestic single phase installs with maximum 16amps generation. They are connected via a Henley Block to the main house tails and there is normally a 100amp supply head fuse.
 
These are domestic single phase installs with maximum 16amps generation. They are connected via a Henley Block to the main house tails and there is normally a 100amp supply head fuse.

So what overload protection is there for the tails of you were to install tails less than 25mm.

There are ways of installing this so that tails suitably sized for the current could be installed instead of the oversized 25mm tails.
 
So what overload protection is there for the tails of you were to install tails less than 25mm.

There are ways of installing this so that tails suitably sized for the current could be installed instead of the oversized 25mm tails.

Hum ...........tin hat on .......... not sure I agree with you ........ sounds like the installation is head, henley block, then off to 2+ CU's ............ a mini CU with a 32A MCB, say for a shower, won't pull over 65A so whats the problem?

bunker time!
 
So what overload protection is there for the tails of you were to install tails less than 25mm.

There are ways of installing this so that tails suitably sized for the current could be installed instead of the oversized 25mm tails.

As I said I am not an electrician so bear with me. I am assuming you mean that if using the 10mm tails for the PV connection they should be fused down at the point of connection rather than using an HB.
 
Hum ...........tin hat on .......... not sure I agree with you ........ sounds like the installation is head, henley block, then off to 2+ CU's ............ a mini CU with a 32A MCB, say for a shower, won't pull over 65A so whats the problem?

bunker time!
Yes, this is the argument that is being used (well similar). I am sitting between an electrician saying it shouldn't be done and a contract engineer that is says there is no issue.
 
If there are spare ways why are you not connecting direct to the dist board.
 
Yes, this is the argument that is being used (well similar). I am sitting between an electrician saying it shouldn't be done and a contract engineer that is says there is no issue.

If they know what they are talking about then they will be able to reference specific regulations to support their point (well one of them will at least)

Who is responsible for the electrical design and certifying the electrical installation for compliance with BS7671 and part P?
Whoever it is they are effectively the person who has final say on this matter.
 
Yes, this is the argument that is being used (well similar). I am sitting between an electrician saying it shouldn't be done and a contract engineer that is says there is no issue.
Ha - tell your contract engineer to apply Ohm's Law to Ze = 0.35 and Uo.Cmin = 218.5V. Then look up the 100A fuse disconnection time and plug that into the adiabatic equation with k = 115.
Spoiler Alert - 10mm tails seem too small (in this situation) to melt the fuse without themselves being heat affected.
 
Hum ...........tin hat on .......... not sure I agree with you ........ sounds like the installation is head, henley block, then off to 2+ CU's ............ a mini CU with a 32A MCB, say for a shower, won't pull over 65A so whats the problem?

bunker time!
Overload protection would not be the issue however if the 10mm tails are adequately sized for fault protection then it’s acceptable as you stated
 
As I said I am not an electrician so bear with me. I am assuming you mean that if using the 10mm tails for the PV connection they should be fused down at the point of connection rather than using an HB.

That’s not what I mean. Overload protection can be installed after the reduction in conductor size in these situations if certain criteria are met.
If feeding a switchfuse or other 1way CU then it can be made to comply easily. If you are leaving spare ways which could be used to feed something else and increase the load then it may be less easy to comply.
 
Ha - tell your contract engineer to apply Ohm's Law to Ze = 0.35 and Uo.Cmin = 218.5V. Then look up the 100A fuse disconnection time and plug that into the adiabatic equation with k = 115.
Spoiler Alert - 10mm tails seem too small (in this situation) to melt the fuse without themselves being heat affected.

See regulations 433.2.2 and 434.2.1, if installed correctly there can be 3metres of reduced size tails between the meter and the CU without upstream fault protection.
 
Ok thanks, that makes a bit of sense. The pv board houses an rcbo for the pv and will have a din mounted generation meter. It will have no spare ways.
 
You must have some design criteria for this want of a better words, lash up.
 
To prevent the chances nuisance tripping the main board.
If you are worried your new install is likely to cause nuisance tripping then you need to reassess what you are doing as the best method is to install directly to the existing dist board providing there are spare ways.
 
If you are worried your new install is likely to cause nuisance tripping then you need to reassess what you are doing as the best method is to install directly to the existing dist board providing there are spare ways.
I wouldnt say it’s the best way if there is spare way on a RCD protected way that shares the same side as a socket circuit for example. It would actually be non compliant due to how long the inverter takes to shut down which can be up to 5 seconds under G83.
 
If you are worried your new install is likely to cause nuisance tripping then you need to reassess what you are doing as the best method is to install directly to the existing dist board providing there are spare ways.

That's VERY wrong for the reason Lee gave above ........... but is the most common method of install I see ......
 
I wouldnt say it’s the best way if there is spare way on a RCD protected way that shares the same side as a socket circuit for example. It would actually be non compliant due to how long the inverter takes to shut down which can be up to 5 seconds under G83.
Where does it state this would be non compliant, not had much to do with these systems so would be interested.
 
I wouldnt say it’s the best way if there is spare way on a RCD protected way that shares the same side as a socket circuit for example. It would actually be non compliant due to how long the inverter takes to shut down which can be up to 5 seconds under G83.
Learning every day.
If I've understood correctly - in a dual RCD board if they've attached PV invertor to MCB under one of the RCDs, if that RCD detects a fault and trips, great. But the invertor continues to put 230V onto the common MCB busbar. So ADS has not been achieved (!!!).
 
Last edited by a moderator:
Where does it state this would be non compliant, not had much to do with these systems so would be interested.

I can’t give a regulation, but plain old common sense should be enough.
If a person receives a shock the RCD will trip, but the PV will continue to supply power to all circuits supplied by that RCD for a period of time, therefore defeating the purpose of the RCD and killing the person.
 
I can see the sense of it now I just wondered if this is quoted anywhere.
 
Regulation 712.411.3.2.1.1 states that on the ac side the pv cable shall be connected to the supply side of a OCPD for automatic disconnection of circuits supplying current carrying equipment
 
Nuisance tripping "might" be a problem when sharing an RCD, but that's the least of the potential issues. More likely (when using transformerless inverters) is that the Type-AC RCD (usually fitted in residential CUs) might become saturated and never trip under fault conditions. That's in addition to the scenario outlined by others relating to the shutdown times of PV inverters and ADS intention of the primary RCD in the first place.....amazing that this topic still causes discussion so many years down the line!! As for the OP's original question, using 10mm2 tails from henley blocks broken into the meter tails (25mm2) is perfectly fine so long as the OCPD on the PV connection is suitably rated. In fact, I'd go so far as to say this is a better method that using a spare way on the non-RCD protected side of the main CU (various reasons including ease of monitoring and avoiding potential issues with RCDs....)

Just my tuppence...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Tail sizes from PV sub-board
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
34

Thread Tags

Tags Tags
sizes

Advert

Thread statistics

Created
CBR600,
Last reply from
SibertSolar,
Replies
34
Views
5,364

Advert

Back
Top