Strictly speaking an unswitched fcu, according to BS5839:1 is not considered a suitable means of isolation as it is not double pole.
Perhaps it was a DP SFCU.Strictly speaking an unswitched fcu, according to BS5839:1 is not considered a suitable means of isolation as it is not double pole.
https://cpc.farnell.com/crabtree/4827-3/switched-fcu-with-neon/dp/PL11960Perhaps it was a DP SFCU.
I think I mentioned that point in post 2A switched fuse spur is not appropriate for an alarm system as it is prone to unauthorized operation.
Thanks very much Pete and everyone else for your input much appreciated
Also got my info wrong at first post the unswitched spur was for a carbon monoxide tester which was fed by a type b 6A is obviously the 3A fuse
And the heating system fed by a type B 6A must be a 5A
If the heating circuit was fed by a type B mcb rated 16A would you bother changing the fuse to a 5A in the fused spur or leave it as 13A?
Depends what else was on the 16 Amp Radial feeding the heating, the supply to the heating could be a leg off the Radial covered by 5 Amp fuse in the SFCU, Don't you think?If the heating circuit was fed by a type B mcb rated 16A would you bother changing the fuse to a 5A in the fused spur or leave it as 13A? Surely you would put it on a 6A type B? If that was the case?
What else is the radial feeding?Everything is being fed via the switched fuse spur but my thought process is if it was below 6A you’d put it on a type B 6A?
What do you mean by everything else is being fed via the SFSU, what else exactly? A single line diagram would clear up your description I'm sure.Everything is being fed via the switched fuse spur but my thought process is if it was below 6A you’d put it on a type B 6A?
I’ve been told you have to select a fuse rating for a heating and hot water circuit on am2 exam but not working on heating or hotwater systems I don’t really know?
Everything is being fed via the switched fuse spur but my thought process is if it was below 6A you’d put it on a type B 6A?
This AM2 seems a right bundle of laughs.On the AM2 you wire it exactly as per the specification they give, I wouldn't be surprised if this also tells you the size of fuse required.
The fuse shoukd be sized according to the load, so work out what the load is and select the most appropriate size of fuse.
As I mentioned earlier for domestic and small commercial heating systems a gas boiler woukd be a 3A fuse and an oil boiler a 5A fuse.
As for the 16A radial, this is the normal circuit to be installed as a dedicated small appliance supply. For a boiler supply you would put a 3A or 5A fuse in the sfcu as required, Yes you could install a 6A radial but this is unusual.
For those of us that have no idea what the AM2 involves , it may have been best to explain this, rather than blandly asking about spurs for heating and alarms, sorry to seem unresponsive it's just how I see things, you must remember for some of us older folk, the AM 2 means SFA, to be blunt it was a distant blot on the horizon that many of us had not heard of.Try and tell the am2 assessors that they want it done the way it says in the design spec..![]()
A fire alarm panel should not be supplied via a switched fused connection unit or an un-switched fused connection unit.
This is what you should be installing.
Also the power supply should be in fire proof cable.
The mcb is a Type B16A to a switched fuse spur in 2.5mm singles and a 1.5mm cpc.
Then from the switched spur goes to a heating and hot water system with a solar panels on it aswell that’s all the spec they give no power ratings anything :/
Try and tell the am2 assessors that they want it done the way it says in the design spec..![]()
Agree good luck let us know how you get on pleaseNo that’s fair enough Pete, completely understand just frustrating they don’t give anymore detail.. don’t think they can fail me on that because they’re not giving me enough informationso fingers crossed
Thanks again everyone for input