Hi, I've been asked to install 13amp supply for a hot tub around 30m from the house.
Supply to property TN-C-S
Plan is to run a 4mm 2 core swa from a 16 amp mcb in the CU to a IP66 RCD switched fused spur (Aprox 25m from house)
Use the armour as the earth until it reaches the Rcd spur in which case I will heat shrink swa and then fit stuffing gland to terminate.
Earth rod with 10mm to the RCD spur and TT the rest.
Any advice would be great
4mm - 13A???
Earth rod - why?
I would fit a socket if the customer is having a hot tub company deliver it as they will only want to see a socket.
I’ve had a few call outs where they have used a standard plug & socket, couldn’t remove the plug as it had melted onto the socket..
One of them shouldn’t have been on a 13a plug, as it was rated at about 3.2 kw.
The hire company had used a commando plug to 13a converter
Heat shrink the SWA? I take it you mean connect the armour to the Earth terminal in the FCU? Advice use a banjo on the SWA and use some suitably sized wire from there to the terminal, If I read your intentions correctly that is not the way to install this SWA, have you done any calculation for cable sizing. or is this a stab in the dark job. a stuffing gland is not the correct method, well you did ask.
For give me if I'm wrong on the earthing arangement.
I have around 80m of 4mm swa in my garage that needs using up should have stated that in original post.
I'm going to have to ring up the hot tub company as it only say on there website 13amp supply. Could really do with a power spec
you will probably find out from the tub supplier/manufacturer that it come with an integrated 10mA RCD in the mains lead. i get the VD on 4.0mm to be 4.3V so it's adequate for the job. ( 11 x 13 x 30 )/1000.
It will be Sat on decking with around 2/3ft surrounding before it turns to grass again
Never done one myself, but it’s a common question raised on here. As said, I read before that some advise with pms supply, to use supply earthing facility AND rod near tub.
Perhaps more learned members can comment on that?
Read a best practice guide on hot tubs which said TT it so I've done that on the few that I've done since.
Having come off the phone to a American bloke who could not not me the power raiding except it pulls 12.8 amps when pumps start.
My installation
16amp mcb from CU to a rcd ip enclosure with rcd fitting inside (drop pme at this point)
Pick up new TT earth
To 25amp rotary is lsolator to the hot tub
Tescos and BM seem to selling a lot of LayZspa hot tubs at the moment.
The Hot tub itself is inflatable, like a large paddling pool.
The pump/heater/bubble maker is a separate unit with quite a long lead which has a 10mA in line RCD.
The pump unit is waterproof, though I have not found an IP rating. The unit has to be next to the tub to connect the pipework and so the controls can be reached.
is the TT earth just cos of the distance from the house? my mate got a jacuzzi hot tub installed a couple of years ago. they insisted on an electrician being on site when it was delivered. but i believe the standard install is just swa from the tub to an isolator switch nearby, and then fed back to the CU with RCD protection.
So if you need to TT will be based on whether if the PEN drops out is there a risk of a return path, from a fault through your body to true earth.
I have a hot tub and I have a PME but I have not TT'd it. The hot tub is all plastic and there is not extraneous conductive parts or exposed conductive parts anywhere near. The water heater is double insulated.
So if there is a fault there is no metallic parts for the live conductor to touch and bring the hot tub to live potential and the water heater is double insulated and it does not actually come into contact with water. It surrounds the plastic pipe that the water travels through.
So in my case installing an earth rod is a completely pointless exercise.
The instructions for the LayZspa require the pump unit to be bonded.
Apparently there’s a connection point on the unit for this.
Thanks for the dumb all I asked was how you would get the 10mm into the spur/FCU an answer would have been sufficient if its advice you want from me then forget it.