Wilko
Hi - this visual info could explain the low IR and would suggest those cables need to be replaced.and the cpcs on the older (pre 2005) wiring are all blackened/carbonised
Hi - this visual info could explain the low IR and would suggest those cables need to be replaced.and the cpcs on the older (pre 2005) wiring are all blackened/carbonised
Blackened?! Any pics? Not familar with that at all. Is the whole place full of oily soot from wok fires or what? That could be a significant factor in low insulation.
Sorry for the delay chaps.....Hi - this visual info could explain the low IR and would suggest those cables need to be replaced.

Same @westward10, I’m starting to think sections have been removed in the pastLooks like it has oxidized. What's it like with the sleeving off.
I'm sure you know that such a low reading is a definite C2, therefore an unsatisfactory outcome on the EICR. Best way to find it is to split ring into sections, and narrow down the location. I recently had a similar result caused by damp affecting several newish sockets and fcus on one particular wall.
The L-E and N-E readings are quite different which suggests everything could be unplugged. I'd now be looking for damaged wiring or waterlogged sockets etc. Splitting the ring in the middle will help narrow things down.
Why do you say a low IR is a C2?
It is up to the inspector to decide upon a Code and this can involve many factors hence BS7671 does not suggest Code designation. Unless the Guidance Note cites a Regulation it is just that, guidance and not a Regulation.