Blackened?! Any pics? Not familar with that at all. Is the whole place full of oily soot from wok fires or what? That could be a significant factor in low insulation.
Hi - this visual info could explain the low IR and would suggest those cables need to be replaced.
Sorry for the delay chaps.....
729870C6-28C2-49E1-900F-534BF7C592F0.jpeg
You can make out the blackened cpc, it’s the length of what exposed/visible but only on the older cable
 
Looks like it has oxidized. What's it like with the sleeving off.
 
The terminal screws are the same. This is normally caused by atmospheric conditions. Are the line and neutrals the same.
 
What kind of state is the extractor system and gas interlock in . They are always a bit gungy, and often burned from lack of cleaning.
Ceramic food heaters are another culprit as wrong cables replaced ones that caused the previous problem. That is usually in chippies though.
 
I'm sure you know that such a low reading is a definite C2, therefore an unsatisfactory outcome on the EICR. Best way to find it is to split ring into sections, and narrow down the location. I recently had a similar result caused by damp affecting several newish sockets and fcus on one particular wall.

Why do you say a low IR is a C2?
 
The L-E and N-E readings are quite different which suggests everything could be unplugged. I'd now be looking for damaged wiring or waterlogged sockets etc. Splitting the ring in the middle will help narrow things down.

your there to do an eicr not put right unless instructed to do so.
 
I am not your mate, we have never met, please do not refer to me as such

I don’t mind you disagreeing with my post, but here it is in GN3, They also hammer that fact home on the 2391-52.

No neimage.jpg
 
Last edited by a moderator:
It is up to the inspector to decide upon a Code and this can involve many factors hence BS7671 does not suggest Code designation. Unless the Guidance Note cites a Regulation it is just that, guidance and not a Regulation.
 
It is up to the inspector to decide upon a Code and this can involve many factors hence BS7671 does not suggest Code designation. Unless the Guidance Note cites a Regulation it is just that, guidance and not a Regulation.


Fair enough and thanks for the clarification. I was just going off what’s currently being taught and tested on the 2391, as GN3 is the bible on that course; and if we’d have coded a low IR reading as anything other than a C2, we’d have been pulled up massively for it.
 