Last week the heating wouldn't come on when called for from Programmer, went into storage and opened the solenoid valve manually and the heating fired up so i assumed the motor was done, ordered a new one. It came yesterday and i swapped it over, a Danfoss HPA2 , 4 core. Thought that would be problem solved but no, when i call for heating it still doesn't come on, yet if i push the valve to manual it fires up.

Any help with where to go next ?

Cheers
 
have you got a voltage tester or a multimetr?
 
Guessing and randomly replacing parts is quite an expensive way of fixing a fault.

The fault could be the programmer, thermostat, loose connection, damaged cable....

You need to carry out some testing to establish what is causing the problem.
 
usually you get 240V when the system calls for heat. check at the wiring centre to see if you get volts on the feed to the actuator.
 
Guessing and randomly replacing parts is quite an expensive way of fixing a fault.

The fault could be the programmer, thermostat, loose connection, damaged cable....

You need to carry out some testing to establish what is causing the problem.

well, i thought was an educated guess tbh, the valve opened manually , they are known to 'go' after a few years , which it has been in for. Fairly common problem/occurance id have thought
 
The brown wire at the valve operates the motor, this should be live when the programmer is on and the room stat is calling for heat.
The grey and orange are the microswitch which closes when the valve is open. Usually the grey is connected to permanent live and the orange is the switched live to the boiler, but these can be the other way round sometimes.
[automerge]1587206400[/automerge]
well, i thought was an educated guess tbh, the valve opened manually , they are known to 'go' after a few years , which it has been in for. Fairly common problem/occurance id have thought

I wouldnt say they are known to 'go' after a few years, obviously they do fail sometimes but often they will last for many years.

The fact the valve opens manually suggests that it is in mechanically good order ruling out the possibility of mechanical failure.

Can you hear the relay in the programmer clicking on and off, can you hear the same in the thermostat?
 
The brown wire at the valve operates the motor, this should be live when the programmer is on and the room stat is calling for heat.
The grey and orange are the microswitch which closes when the valve is open. Usually the grey is connected to permanent live and the orange is the switched live to the boiler, but these can be the other way round sometimes.
[automerge]1587206400[/automerge]


I wouldnt say they are known to 'go' after a few years, obviously they do fail sometimes but often they will last for many years.

The fact the valve opens manually suggests that it is in mechanically good order ruling out the possibility of mechanical failure.

Can you hear the relay in the programmer clicking on and off, can you hear the same in the thermostat?

There is nothing on the brown when I call for heat.

Both zone valves for heating and hot water, the orange and greys are paired together in terminals 6 + 7 of junction box

All looks ok, no loose connections or anything untoward
 
There is nothing on the brown when I call for heat.

Both zone valves for heating and hot water, the orange and greys are paired together in terminals 6 + 7 of junction box

All looks ok, no loose connections or anything untoward

Can you clarify what you mean by 'nothing on the brown'?
 
Are these of any help? Taken from the Honeywell app, might be worth downloading.
 

Attachments

  • 25501382-4811-442A-9126-964A839C36CB.jpeg
    25501382-4811-442A-9126-964A839C36CB.jpeg
    82.1 KB · Views: 8
  • 70E9BBA0-9D74-4488-A3E4-1F5D5DF8C894.jpeg
    70E9BBA0-9D74-4488-A3E4-1F5D5DF8C894.jpeg
    70.9 KB · Views: 8

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Caithness
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
No heating , changed Solenoid valve
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
SteveTheSpark,
Last reply from
Boiler Repairs,
Replies
14
Views
2,529

Advert

Back
Top