Hey , new to forum so not sure how it all works but here goes

Last week the heating wouldn't come on when called for from Programmer, went into storage and opened the solenoid valve manually and the heating fired up so i assumed the motor was done, ordered a new one. It came yesterday and i swapped it over, a Danfoss HPA2 , 4 core. Thought that would be problem solved but no, when i call for heating it still doesn't come on, yet if i push the valve to manual it fires up.

Any help with where to go next ?

Cheers
 
have you got a voltage tester or a multimetr?
 
Guessing and randomly replacing parts is quite an expensive way of fixing a fault.

The fault could be the programmer, thermostat, loose connection, damaged cable....

You need to carry out some testing to establish what is causing the problem.
 
usually you get 240V when the system calls for heat. check at the wiring centre to see if you get volts on the feed to the actuator.
 
Guessing and randomly replacing parts is quite an expensive way of fixing a fault.

The fault could be the programmer, thermostat, loose connection, damaged cable....

You need to carry out some testing to establish what is causing the problem.

well, i thought was an educated guess tbh, the valve opened manually , they are known to 'go' after a few years , which it has been in for. Fairly common problem/occurance id have thought
 
The brown wire at the valve operates the motor, this should be live when the programmer is on and the room stat is calling for heat.
The grey and orange are the microswitch which closes when the valve is open. Usually the grey is connected to permanent live and the orange is the switched live to the boiler, but these can be the other way round sometimes.
[automerge]1587206400[/automerge]
well, i thought was an educated guess tbh, the valve opened manually , they are known to 'go' after a few years , which it has been in for. Fairly common problem/occurance id have thought

I wouldnt say they are known to 'go' after a few years, obviously they do fail sometimes but often they will last for many years.

The fact the valve opens manually suggests that it is in mechanically good order ruling out the possibility of mechanical failure.

Can you hear the relay in the programmer clicking on and off, can you hear the same in the thermostat?
 
The brown wire at the valve operates the motor, this should be live when the programmer is on and the room stat is calling for heat.
The grey and orange are the microswitch which closes when the valve is open. Usually the grey is connected to permanent live and the orange is the switched live to the boiler, but these can be the other way round sometimes.
[automerge]1587206400[/automerge]


I wouldnt say they are known to 'go' after a few years, obviously they do fail sometimes but often they will last for many years.

The fact the valve opens manually suggests that it is in mechanically good order ruling out the possibility of mechanical failure.

Can you hear the relay in the programmer clicking on and off, can you hear the same in the thermostat?

There is nothing on the brown when I call for heat.

Both zone valves for heating and hot water, the orange and greys are paired together in terminals 6 + 7 of junction box

All looks ok, no loose connections or anything untoward
 

Reply to No heating , changed Solenoid valve in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
584
(Or that might be should a failed HW valve keep boiler running) Woke up this morning to find the boiler still running even though all timers off...
Replies
4
Views
982
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
949
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
889

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock