Evening all.

Couple of PIRS today, which i generally try and avoid at all costs :D

Anyways, typical lighting circuit switch drops with no cpc's, however, lighting circuit has.

How would you code this?

Bearing in mind, there is no RCD protection to the circuits.

Cheers.:cool:
 
Are there any Class one fittings attached to the CPC less' switch dops at the time of your test mate???
 
With switch drops I'd be concerned about the exposed screws connecting to the metal bacboxes with no CPC.... or is that just rubbish?
 
Code 4 does not comply with 17th edition,class 2 switches only and maybe a warning notice at ccu
 
I would code 1 that if there's no RCD.

One flat has a 16th CU, the other an old wylex, which will be replaced, that can easily accomodate an RCBO. Also, most of the back boxes are metal with plastic threads.

Are there any Class one fittings attached to the CPC less' switch dops at the time of your test mate???

No none at all.

With switch drops I'd be concerned about the exposed screws connecting to the metal bacboxes with no CPC.... or is that just rubbish?

I wouldnt say it was rubbish, however, there is a chance that the line could come into contact with the box under a fault, especially if it gets trapped with the screw somehow.
 
In my mind, at the time of test it would warrant a code 2, as IMO it does require improvement. Particularly as these are rented premesis (I think???) and you could not guarantee that the tennants would mess about with em.:rolleyes:
 
Yes i tend to agree with you.

They are rented out to students at the mo and the owner wants to now put families in there.

I was thinking of quoting to replace the switch drops in MT1 and mount surface switches in place of the flush.

She seemed happy with that.
 