So was testing a house today (new build)
When I came to testing on of the ring finals in the house, when testing insulation resistance the live and earth legs on the ring are clear but live to the earth on cpc’s on the cooker circuit, other ring, downstairs lights and heating its bang down I’m thinking something to do with damp walls? But every time Other circuit tested out fine on IR
What I meant was if for say the cooker circuit you did:
L to N and got >999mohms
N to E and got >999mohms
And L to E gave 0mohms
then you can be pretty sure there’s a dead short somewhere as
1) any dampness would not cause zero anyway
2) any dampness would be unlikely to affect just one core
So I would then use the (low resistance) continuity function to measure more accurately what the resistance is between L and E. That can then give you some idea where the fault is.
As there’s a rfc affected, if you take both ends out of CU and measure L to E on continuity at the sockets the resistance should drop as you get nearer the fault and the fault will be between the two lowest readings.
It interesting that so many circuits are apparently affected. Forgive the silly question but are you testing in the top of the breakers and are the breakers all off?
For the cooker circuit all tests are clear including L-E the only one that’s down is L on the sockets the other cps I was disconnecting the cpcs one at a time from earth bar
For example
Clip on L from sockets circuit then clipping onto cpc for cooker that’s down
All breakers off just in the top individually testing them to earth
Basically 0 M ohm
Are all the conductors under test dissed from the CU INCLUDING THE MAIN EARTH During testing?
For example
Normally you IR test with all CPC connected to the MET so a fault from, say, L to some wet brickwork will appear. Only then would you remove the CPC for that circuit to try and find out if the fault is L-CPC or L-Earth somewhere.
I see @Pete999 just posted about that!
They was all connected to start with then I started disconnecting some then still testing via the MET to see which cpcs were bringing it down
Retford
Trainee Electrician
Live earth fault??
Kyle_Trainee,
timhoward,