I have just had a "smart" meter installed , and at night the electrics trips the RCD when the night storage radiator section comes on. I have had them out and they said installation was correct. I know a little about electrics (more over cautious and basic) but was suppressed when I looked at the lay out for the Night storage CU that the neutral goes through the RCD but the live goes direct - could this be a cause for the RCD to be triggered. I will have to get an electrician out to check all the wiring for the storage heaters if I cannot persuade them they have done something to suddenly make my electrics trip when that CU is on. Everything else seems to work fine. I have attached a simplified circuit diagram - electrics in the house have always been a little spaghetti junction, but never had any problems. Local electrician has always installed new stuff properly. Can anyone help? or suggest what my problem could be.
If I turn the CU for the night storage radiators off - then I get electrics 24/7 - if I turn that batch on then it pops overnight.
Hi. If your diagram is right, and i have to say it looks to be, then I agree that isn’t going to work.
As you said the N split is the wrong side of the RCD (which is acting as fault production for the older consumer unit which has no RCD and you probably have an Earth rod - a TT setup).
My guess is that the henley block under the rcd was originally used to split the Neutral. It’s now used pointlessly to split a Live.
I’d try calling them again.
They have certainly messed up in my opinion but it might be quicker to get a sparks to fix it as the issues are all downstream of the meter tails. Then write a letter of complaint!
Reactions: Dartlec
Thank you, as I said my basic knowledge of electrics - and gazing at it - I think the people who install, and the person who came out to look at it are not electricians - more installers - if that make sense.
Meter Monkey is a more accurate title.
An rcd works by sensing an imbalance on the current on the live and neutral. If the difference is over the threshold of, I would presume, 30mA, the rcd trips…. As far as it knows, the spare amps are going to earth, and it’s doing what it’s meant to.
when your off peak comes on, whatever load on the live is not detected at all by the rcd, but the neutral is…. As it should be balanced, it’s tripping out.
Are you using any off peak heating just now? It might be worth testing by turning the off peak board off completely and seeing if the rcd holds as no load at all will be going through.
If I turn all CU for the night storage radiators off I get uninterrupted power for the rest of the house - only issue is if I leave the storage heater bit on - it then trips when the power to that bit kicks in. Your comments confirm my suspicion that sending the neutral through the RCD and the live direct is causing the problem.
Reactions: timhoward
Thank you all for your replies, I have contacted the meter installer lot, hopefully they can rewire the bit where they made the error. I expect they are not used to installing in an old property with old mechanical meters, three CU, one of which is for night storage radiators. I did jokingly ask if they could send an electrician this time, and they did say they did not have any of them, just installers. You would have thought they could have some trouble shooting electricians to help out.
Reactions: DPG and Dartlec
Great, it isn't in fact too complicated to sort.
It just needs a henley block in the N from the cut-out BEFORE the RCD, then the N to the off peak CU removed from the top henley block, shortened and put in the new henley block.
(Though if they are pulling the fuse, they may prefer to run a new off-peak tail and re-purpose the block underneath that's there)
Up to them anyway!
Reactions: Dartlec
These not so smart smart meter installers clearly are not trained to install on anything but the simple jobs and also work to the if you don't know ask principle
I wonder how many smart meters are actually installed where there are issues with the DNO equipment like main earths missing that are never addressed, the installation of smart meters would have been a good opportunity to get an overall assessment of the state of the installed distribution throughout the UK but the quality of the installers means it isn't going to happen
Up to them anyway!
I think I can see a slightly old TN-S setup under the main head, in which case this is the way to do it.
It's just possible that you are on a TT (earth Rod) - in which case you may need a functioning RCD on the storage heater circuits too to ensure fault protection is working. Alternatively it may be possible to get the DNO for your area to upgrade the earthing to PME.
It may be worth getting an electrician to check things over generally - it may be sensible at some point in the not too distant future to look at updating things a little, especially if you are likely to be doing any electrical work in the future....
Nothing wrong with what you have at the minute, assuming that the RCD is tested regularly with the test button. Just that it is probably >40 years old at this point.
They will admit it themselves when I've talked to them - they have a plug in socket tester and a non contact voltage tester for verifying polarity - that's it...
I agree that it would have been a great way for the DNOs to update their records to actually comply with their legal requirement to provide the details of fusing and earthing on request...
Taking another look at the pictures if the meter tails were taken from the RCD and connected into the henley blocks above the CU and the CU tails taken from the henley's and connected to the RCD that would be a better fix as the CU to the right already has an RCD in it
This is the second recent thread where the smart meter installer has cocked up the off peak supply.
Duh!
Smart meter, dumb installer.
Very sensible comments, I ought to get someone in to take a fresh look at the setup at some point, although the installation of a smart meter has not helped. The original unit was looking old when we moved in some 30 years ago! We do have an earth rod, massive thing stuck into the ground. The other thing I did not mention was the "smart" meter does not work as it will not connect to their network (is it mobile phone?) so all this fuss and it is not reporting back to base - expect I will have to read this meter somehow for them!
So a not very-smart-meter, installed by a not-very-smart installer - excellent!
The earth rod may not be providing the only earth, but if it is, you may well need RCD protection on the storage heaters - or need to get the earthing upgraded by the DNO (who will sometimes do so for free).
It can be tested easily enough by someone with the right meter - may be worth finding a decent local electrician to just have a quick look over things - won't take very long to get a good idea of the installation and whether it's an issue or not...
But the meter installer should be coming back to resolve the issue they caused in this case anyway...
It's funny how when working off photos you can have all the right questions and get the answers totally wrong....
I was thinking "Is it TT, and do you need an RCD for the off-peak CU". Yet managed to miss the (likely) TNS connection and thought the off-peak CU had an RCD because there's a similar CU in a picture which does have an RCD.....
I'm glad other people were on the ball!
So does the live that goes to the storage heater CU need to go through the RCD - so instead or removing the neutral from going through the RCD - send both live and neutral through the RCD? I can see I need to get an electrician out after the meter installing team have finished.
Oh dear I've confused things even more....sorry....
1 - main things is that it has to work again, and splitting the N before the RCD is almost certainly how it was before, and this is how I'd put it back. Alternatively the L could be moved to other side of RCD. That works too.
2 - There's a secondary question of the earthing arrangements, if it's what we all think it is and what it looks like, there is no issue, and lack of RCD protection for storage heater CU is not the end of the world, just something that's advisable these days.
If on the other hand the earthing is really all from from the earth electrode then the lack of RCD protection would be a considerably bigger deal from a safety point of view.
I hope that clarifies things a bit! Basically let the meter people make it work again, and then best to get someone to check it over.
Due to the age of the installation, i'd have someone in checking the RCD works for a start.... There are a lot of circuits coming off it as it stands, and adding the off peak CU through it too, could push it over the edge regarding cumulative earth leakage.
The "meter installers" have cocked this one up, and they need to fix it before you need to use the heating.
That's exactly why I'd favour splitting the Neutral, coupled with my natural self-preservation tendencies to touch as little as possible so I can't be blamed for the next problem ... ?
The Off Peak Live (and Neutral) and and Normal Live (and Neutral) can't both go through the existing RCD.
Either the Off Peak Live and Neutral need to miss out the existing RCD, which is how they must have been before the Smarties turned up.
Or the Off Peak needs it's own new RCD.
Makes things very clear - and the need to get someone who knows what they are doing in once the meter fitters have done their job even clearer.
Reactions: Jim_e_Jib
From all the comments
My thoughts are to try to get them to take the live and neutral (neutral coming from a split) direct to the Storage radiator CU. To have normal main and neutral split - so one lot goes direct to the newer CU (one with internal RCD) and another lot going via the external RCD to the old CU. Then presumably I need a proper electrician to come and check it all over - with a view to putting in a RCD for the storage radiators.
I feel I may need to draw them a diagram and maybe put string on to explain where things go - LOL
They don't want to KNOW what they already suspect so they send out these "installers" as they are not going to raise too many issues.
  • Dislike
Reactions: UNG
get a sparks to put the meter mong's work back right so it all works. then decide on the way forward.
  • Winner
Reactions: UNG
Thought I would update you on this. They have been out and rewired the storage heater CU - did take me having to stop the chap and telling him what to do - he then had to contact his manager to get permission to do the wiring. But I think he understood why it was tripping by the time I had gone through how a RCD worked and that they had miswired my CU. I have had a chat with a friend of mine who is an electrician and he tells me it is unusual to wire the CU for storage radiators through an RCD. He agreed that the main CU is fine but that he needs to move the wiring to the CU that has an RCD as it is more likely to trip and on minor bits rather than what it is built to pop on. I agreed to drop my case with the electric lot for £450 compensation - and I will pay to have the wires moved. So end of this saga! Thank you all for your comments - I think without them I could still be battling the electric company.
Thanks for the update, hope all is (going to be) working O.K now.
Reactions: Brian N and DPG
I did explain to the Manager of the complaints lot that it seemed very strange they would not come out until my electrics had gone off two days in a row - he said he would look into that policy, as he agreed that seemed wrong. I pointed out that if it appeared that the wiring may be at fault then they should have an electrician who could come out and double check the wiring- as clearly I had 3 people out - the first failed to wire it correctly and the following two had no idea about electrics. I doubt anything will change - still I should be able to buy a good amount of wine even after paying my electrician friend for doing the rewire - especially as I removed a wasp nest for him a few years back.
Reactions: DPG and loz2754
I went up into a loft on a new build once when the plumber was testing his newly installed heating system. Vent pipe over the header tank was gushing full bore, and splashing water everywhere.
Had to take a sheet of cardboard and a black marker pen, and draw out for him how he should have connected the tank. Pretty sure he didn't understand a word I said, but he changed it to my diagram anyway.
New smart meter, storage heaters now trip RCD