Spent 6hrs today trying to find a break in a ring circuit and why it kept tripping the RCD
I think I need to make a mental note next time to check for spurious junction boxes in the shower.

After spending an hour rummaging around the loft (it was a bungalow) tracing cable routes, which in itself was no mean feat as it was like a snake mating ball up there.
I traced a cable from a socket going down into the bathroom.
So I went into the bathroom and found this on the opposite wall to the shower above the bath..
Alarm bells started ringing when I saw the wood screws rather than machined screws.
When I took the cover off I found the problem.
Lives just touching but not even taped. Neutral was the same although they at least had some tape over.
Apparently this was done by a qualified electrician…. (Del’s famous quip springs to mind here).
But I don’t doubt it wasn’t the little old dear that lived there.
Having done all the usual ways of testing a ring to find a break I was baffled as to why I couldn’t find it. Which is why I eventually went up in to the loft and started moving boarding and insulation to check the cable routes.
Obviously I wasn’t expecting some plank to have done a joint in a bathroom. Well at least trying to!