Slow to the party, going back to that fire alarm…
1- I wouldn’t want to be that last one that touched that.
2- isn’t there also a band 1 and band 2 voltage in same containment issue? 24v dc and 230v ac in same trunking?
3 - as above the sounder circuit setup isn’t correct
4 - Hope it’s on its own circuit. At least stick it on an unswitched spur - you don’t want someone switching off the fire alarm. I’m out of date but I believe Bs5389 mandates a red key switch these days?
The alarm monkeys should be putting this right and taking responsibility for it!
missed out on a EICR as himeowner's insurance insisted on NICEIC or Napit. he missed a couple of things, this being the worst.
2- isn’t there also a band 1 and band 2 voltage in same containment issue? 24v dc and 230v ac in same trunking? OK as long as all cables are rated the same voltage. i.e. in this case 230V+
Panel should have been mounted uo against the trunking, allowing just for trunking lid. then no unsightly FP drops.
So likely didn't remove cover at all then!
(and thanks for reminding me that if the cable is insulated to the highest voltage present that reg is satisfied.)
Don't barristers work with briefs so just call it a little bit of research for work
He will probably deny all knowledge of them, but if you look you will see insulation on his knees :)
Back to work after Covid, and started on a kitchen that should have started last week.
Builder has already been in, ripped out the the old kitchen, tiles, flooring… the lot.
Which left the electrics in not the best condition.
The owners have moved out, so there was nothing stopping him attempting to turn things off at the board…
Switches and sockets hanging on cables where he’d taken a wall down… other sockets broken where he’d struck them with a hammer when taking tiles off…. And taped up cable for oven, with the cooker switch on!
Oh, and old extractor point removed… cables taped up separately…. Leaving the rfc as an incomplete ring.
a proper builder would have used sellotape on those ends, not electrical tape.
Zoom in on the pic with the cooker switch…. Over to right. The outlet has been taken off and wrapped in tape. The tape has come off a bit and there is bare, live copper showing.
I suppose saving grace is a full RCBO board had been fitted earlier in the year….
Reactions: nicebutdim
Fortunately RCD protected but a nurse thought she'd help out by replacing the diffuser on this light.
I've a real concerns when it comes to old fluorescent lighting, the heat generated eventually perishes all the plastic components.
In this case its the permanent live terminal that has just crumbled away.
On Monday I did one where the incoming cables had melted to the ballast.
More of a heads up than dodgy work.
Class 1 exterior light only works when the fan comes on……and then the vent flaps set off the sensor 😂😂….peaky cpcs are overrated anyways😳
On a more serious note the builder that did this and much more just got an 18th suspended sentence for signing off the electrical install of which this is part despite not being an electrician or a member or a scam….he gave the customer an NICEiC form AND signed it in his name 😬😂
View attachment 99520View attachment 99521
I wonder if anything would have come of it if he had got a cert from tool station instead
Reactions: Baddegg
18 sentences for the same type of offence and each one suspended?
Nothing at all wrong with the justice system it would seem.
Reactions: Baddegg
The electrics are only the half of it, I’ve been in the building trade a long time and this build is by far the worst I’ve seen….another example is the pitched roof is just covered over with osb and then the tiles screwed directly to it!….I wish I was joking honestly 😩…..surprisingly it leaks a little 😂……he has concreted straight over the main sewer pipe twice on each side of the extension, that cheered up building control no end….
I love it when I get asked to check a board and when I arrive I get told the kitchen fitters did an outstanding job with the electrics...
Well they thought so until I started to point out a few 'anomalies' 😇
CPC's in the way? Just cut them short..
It's in a cupboard so it's ok....
Underfloor heating doesn't work for some reason.....
Lets see now:
Mixed MCBs,
4 conductors shoved into one MCB - though they are all held tight. Not sure if it's the clamp of the fact the cables have no space to move!
End MCB split
Not a lot of room for cables and I'm guessing they don't understand what happens when cables are loaded and they warm up!
And they clearly haven't heard of diversity for that RCD!! Which is supplying:
1 x 40A Shower
1 x 32A Induction Hob
1 x 32A Oven
1 x 32A Kitchen Ring
1 x 32A downstairs ring
1 x 32A upstairs ring
But they have used Hager accessories to match the MCBs and the finish in the kitchen was quite nice....🤨
Pattress box buried in the wall?
"outstanding" isnt the word i would use
Lets see now:
Mixed MCBs,
End MCB split
1 x 40A Shower
1 x 32A Oven
Guessing that 63amp RCD will never be pushed past its 63amp rating if you have a lot of faith, taking that shower while the partner has got all the Xmas dinner cooking in the electric oven and on the electric hob, luckily diversity has a hand but it ain't always that accommodating, lets not forget the gas boiler going faulty and plugging in a few convection heaters in.
Reactions: pc1966
Not an electrical job but a new bathroom installation
I could not believe they got away with installing the towel rail the way they did
lol!
lol!
Do you blame the customer for accepting it or the bodger who did it and thought it was an acceptable job
lol!
It amazes me that anyone would do this, its just as easy to do it right in the first place, so why go to the effort of bodging it so badly?
Crazy!!
Glad you shared this by the way :)
Reactions: pirate and DPG
Trouble is some customers haven't a clue what they are looking at, they only see the shinny bits rather than the detail.
8K
Darkwood,
mainline,