Hi all any advice welcome.
Long story but at the last moment I have been asked to advise on the possibility of installing electric ufh in a large yoga room as bums are cold on the floor.
Room is 90sqm but my thinking for easy install supplier does 12sqm mats so perimeter left out that is 2x mat per phase giving 72sqm of load at 150w psqm. Not looked at 3 phase loading for a while but instead of taking 3x single phases to the plant room was thinking of a 3 phase 6mm rcbo supply(distance) from consumer unit to local isolator then contactor and single supplies out to 2x mat per cable/phase. Load would be balanced but still been domestic for so long thinking about the neutrals.
Sorry post got a bit long, hope you get the gist 😂 thanks
I appreciate that but maybe I'm thinking too much, I was thinking of 6mm 3 phase to the plant room then 4mm te out to a pair of mats. Therefore in my mind it's balanced so the original 6mm neutral would be fine for all the single phase loads
Why 4mm?
Personally if I was doing this I'd probably run a TP supply to a small enclosure with seperate protection for each mat, take a supply from there to feed what ever control system is required and control the mats via a contactor.
Protecting each mat seperately makes things easier when they start to fail.
Why 4mm?
4mm l(ength of run) , my thinking originally was 3 phase to the contactor then out in 4mm te each phase to an enclosure with 20amp protection for each set of two mats. Stat to control the contactor
I though it was still permitted to run a reduced size neutral for balanced loads?
I think it is, however when choosing between 4 and 6mm cable, why would you bother?
also, if you are splitting the load up into 3 identical single phase loads, you can’t guarantee they are ballenced, turn off one or two breakers and your undersized N might be in trouble?
Why 4mm?
Thanks both, 6mm is oversized for 3 phase but was thinking of it possibly being unbalanced. So now thinking 6mm swa 3 phase to an isolator, then out to single phase protection for mats / control circuit then to single phase contractors instead of a 4 pole one via stat.
What has it being unbalanced got to do with oversizing the cable?
A balanced 3 phase system the N load is zero, reducing the load on any phase will increase the N current.
worst case Is all fully loaded on one phase and nothing on the other 2, the N current will then equal the phase current.
Yes total load decreases but the imbalance increases, as I say not looked into the phase for many moons. Just remember we had to balance it best as possible
Yes it will become imbalanced but that doesn't increase the load!
With an unbalanced load there will be some neutral current, but with simple resistive loads the neutral current will never exceed the line current no matter how far out of balance it is.
Is this a three core with a half sized neutral.
Found a picture
Learn something new everyday but they look to the eye like sectorial aluminium with AWA in fact I'm convinced it is AWA.
Learn something new everyday but they look to the eye like sectorial aluminium with AWA.
I know what you mean, but that was the second time I encountered this stuff. The first time I was a little perplexed and had to make a few phone calls.
In my vast experience of terminating just one sectoral Al armoured cable the armour was of a more rectangular section and not round like it is in SWA.
To my eye but you have physically seen it the outer face of the strands in the pic look flat which to me says it is not steel. Nevertheless I have never seen that before.