Hi all any advice welcome.
Long story but at the last moment I have been asked to advise on the possibility of installing electric ufh in a large yoga room as bums are cold on the floor.
Room is 90sqm but my thinking for easy install supplier does 12sqm mats so perimeter left out that is 2x mat per phase giving 72sqm of load at 150w psqm. Not looked at 3 phase loading for a while but instead of taking 3x single phases to the plant room was thinking of a 3 phase 6mm rcbo supply(distance) from consumer unit to local isolator then contactor and single supplies out to 2x mat per cable/phase. Load would be balanced but still been domestic for so long thinking about the neutrals.
Sorry post got a bit long, hope you get the gist 😂 thanks
 
I appreciate that but maybe I'm thinking too much, I was thinking of 6mm 3 phase to the plant room then 4mm te out to a pair of mats. Therefore in my mind it's balanced so the original 6mm neutral would be fine for all the single phase loads

Why 4mm?

Personally if I was doing this I'd probably run a TP supply to a small enclosure with seperate protection for each mat, take a supply from there to feed what ever control system is required and control the mats via a contactor.

Protecting each mat seperately makes things easier when they start to fail.
 
Why 4mm?

Personally if I was doing this I'd probably run a TP supply to a small enclosure with seperate protection for each mat, take a supply from there to feed what ever control system is required and control the mats via a contactor.

Protecting each mat seperately makes things easier when they start to fail.
4mm l(ength of run) , my thinking originally was 3 phase to the contactor then out in 4mm te each phase to an enclosure with 20amp protection for each set of two mats. Stat to control the contactor
 
I though it was still permitted to run a reduced size neutral for balanced loads?
I think it is, however when choosing between 4 and 6mm cable, why would you bother?
also, if you are splitting the load up into 3 identical single phase loads, you can’t guarantee they are ballenced, turn off one or two breakers and your undersized N might be in trouble?
 
Why 4mm?

Personally if I was doing this I'd probably run a TP supply to a small enclosure with seperate protection for each mat, take a supply from there to feed what ever control system is required and control the mats via a contactor.

Protecting each mat seperately makes things easier when they start to fail.

I think it is, however when choosing between 4 and 6mm cable, why would you bother?
also, if you are splitting the load up into 3 identical single phase loads, you can’t guarantee they are ballenced, turn off one or two breakers and your undersized N might be in trouble?
Thanks both, 6mm is oversized for 3 phase but was thinking of it possibly being unbalanced. So now thinking 6mm swa 3 phase to an isolator, then out to single phase protection for mats / control circuit then to single phase contractors instead of a 4 pole one via stat.
 
Thanks both, 6mm is oversized for 3 phase but was thinking of it possibly being unbalanced. So now thinking 6mm swa 3 phase to an isolator, then out to single phase protection for mats / control circuit then to single phase contractors instead of a 4 pole one via stat.

What has it being unbalanced got to do with oversizing the cable?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Forest electrical

Thread Information

Title
Large electrical ufh install
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32
Unsolved
--

Advert

Thread statistics

Created
sclarkin,
Last reply from
davesparks,
Replies
32
Views
2,870

Advert

Back
Top