Hi all any advice welcome.
Long story but at the last moment I have been asked to advise on the possibility of installing electric ufh in a large yoga room as bums are cold on the floor.
Room is 90sqm but my thinking for easy install supplier does 12sqm mats so perimeter left out that is 2x mat per phase giving 72sqm of load at 150w psqm. Not looked at 3 phase loading for a while but instead of taking 3x single phases to the plant room was thinking of a 3 phase 6mm rcbo supply(distance) from consumer unit to local isolator then contactor and single supplies out to 2x mat per cable/phase. Load would be balanced but still been domestic for so long thinking about the neutrals.
Sorry post got a bit long, hope you get the gist
thanks
Long story but at the last moment I have been asked to advise on the possibility of installing electric ufh in a large yoga room as bums are cold on the floor.
Room is 90sqm but my thinking for easy install supplier does 12sqm mats so perimeter left out that is 2x mat per phase giving 72sqm of load at 150w psqm. Not looked at 3 phase loading for a while but instead of taking 3x single phases to the plant room was thinking of a 3 phase 6mm rcbo supply(distance) from consumer unit to local isolator then contactor and single supplies out to 2x mat per cable/phase. Load would be balanced but still been domestic for so long thinking about the neutrals.