This is not necessarily correct. The scale of building and footfall may permit a single means of escape.
In general there should normally be at least 2 escape routes but in certain circumstances one is acceptable. One example is if a part of the building only accomadates up to 60 people, there are other points to look at but the fire officer would be able to give more advice. If you are on the first floor or above you would expect two or more and each would be independent from each other.
You stated there must be two means of escape, this is not correct. I am well aware of building requirements.
Yes. Wrong choice of wording. But i would in general like to see two escape routes and if there isn't I look at the one and make sure it complies.
Sounds to me like several things may be being confused:
Fire exit door - a means to escape the building when there is a fire. Needs appropriate signage, lighting and door handles to help people exit in a hurry. I would have thought the rules don't care if the door is open or not when there is no fire.
Fire door - a door that needs to resist the spread of fire. Often between fire compartments in a building. These need to be closed when there is a fire to do their job. Various ways are used if making sure they are closed in a fire are used like signs saying "keep shut", springs that close the doors, automatic closing doors etc
It sounds to me like the problem may be that it is a fire door and that the way they are ensuring it is closed in a fire is by keeping it locked shut. Are there springs/door closers on the door so that it closes automatically when you do open it?
Whether it be a Fire door, Disabled access, Fire Escape or just a door, it's easily opened in an emergency.
The manager may have other reasons for not wanting the door open, such as security, or maybe It's just to stop the mess that's been left there.
I think the confusion is that whether the door is an emergency exit or not, the issue is that the staff would like the door open for fresh air, the manager says no, and is giving the excuse that it’s a fire door and must remain closed…. And to clarify his position, he’s padlocking it shut.
I asked earlier whether there was adequate ventilation…. If not, it’s an HSE issue.
My 17yo daughter is working at a factory for summer and I just found out there’s only 2 toilets… (1 unisex, 1 disabled) for over 50 staff…. So I might be reading up on HSE more than I should recently.
Nope, no springs on the door. Also it's a disabled access door.
Is there a refuge for disabled people in the event of an emergency.
djm0057,
davesparks,