aesmith
Hi,
Our solar inverter is connected to a dedicated circuit from an RCBO in a CU in our garage. The RCBO was chosen, supplied and installed by the solar installers. The cable runs up from the CU in plastic trunking, goes through a concrete block wall to the next room, then is clipped to the wall and along a purlin at ceiling height before dropping down to the inverter in plastic conduit.
Since installation last May the RCBO has tripped twice for no apparent reason. I haven't had any feedback yet from the installer, but after the first trip they said there was no indication of any fault with the inverter. I have suggested that they replace the RCBO just for elimination.
However looking at information from the manufacturer, Solaredge, it seems they're not particularly keen on an external RCD. They recommend that if one if fitted it should be 100mA or 300mA, and there's a comment that where "local codes" require a 30mA RCD then there may be nuisance trips.
But before exploring that further I'd just like to confirm the current requirements. From what I've described, does it sound as if RCD protection is required on that particular circuit cable run?
Thanks,
It possibly doesnt need one.
Under the regs, a circuit would need RCD protection if any of the following were true
Supplies sockets not exceeding 32A
Passes through, or serves a room containing a bath or shower
Any circuit with luminaires (lights)
Is buried in a wall less than 50mm deep*
*This is the one that covers basically everything in a newbuild house... but if you say the cable is surface run, even in trunking...... it may not be required.
The installers, however, may have their own procedures that EVERYTHING must be RCD protected whether it requires it or not.
Hi,
Thanks,
What's the model number ?
Most inverters will have an internal rcd
These inverters by construction cannot feed DC fault current into the installation, as required by IEC 60364-7-
712:2002.
I would change the rcd to a type A 100ma, as suggested by the manufacturer.
712:2002.
Thanks. It's a Solaredge "Home Hub" inverter model SE6000H-RWBMNBF54.
If the Wiring Regulations say an RCD is needed, doesn't that mean it needs to be 30mA?
Type of earthing (ie:TT) could require (RCD) Residual Current Device to meet disconnection times,also buried in walls,passing though bathroom or supplying standard sockets will require one.little spark explains this better above
Thanks. Earthing is TNS. The circuit runs entirely within a detached outbuildings, from the garage into an adjoining utility room where the solar gear is installed. Does passing through a wall perpendicular to the surface count as buried in the wall?
No, it doesn't. (It's a fair question though!) You're all good
OK thanks. I don't want to go against the installer's opinions, but I think I will suggest to them that the breaker could maybe be changed to an MCB.
Thanks for all the comments. I've had some feedback from the installers, they say they're going to replace the RCBO as current rules say it needs to be "bidirectional". A quick search around for myself, all discussion about bidirectional devices relates to RCDs or RCBOs. Does that mean an MCB can't be used? Or are MCBs inherently bidirectional?
Thanks. I know there's a risk I'm going to come across as a smart alec talking to the installers in this detail, I just don't want to be an incorrect smart alec.
Is it an A or AC RCBO? I've fitted plenty of type A RCBO's on Solar Edge inverters and never had a nuisance tripping issue. Prior to the new requirements they were not Bi-directional.
Clause 6 .1 (Standard marking) of BS EN 60898-1:2019 requires that:
If it is necessary to distinguish between the supply and the load terminals, the former shall be indicated by arrows pointing towards the circuit-breaker and the latter by arrows pointing away from the circuit-breaker.
In the case of RCCBs and RCBOs, Clause 6 (Marking and other product information) of BS EN 61008 1:2012+A12:2017 and BS EN 61009-1:2012+A12:2016 both state:
If it is necessary to distinguish between the supply and the load terminals, they shall be clearly marked (e.g. by "line" and
"load" placed near the corresponding terminals or by arrows indicating the direction of power flow).
Currently it's a Hager ADA332G which I see is described as "Type A(AC & Pulsating DC Sensitive)"
Many RCBOs do not switch the neutral and so would not be suitable for use to provide additional protection to the AC supply cable to the PV system.
Thanks. Back to basics I think I'm clear that the actual circuit cabling doesn’t require RCD protection, and Solaredge don't recommend it. So does the requirement to disconnect both L and N apply if we just had an MCB type breaker? To be honest I'm not sure how we could comply, it's a Hager DB and as far as I can see neither Hager RCBOs nor MCBs disconnect N.
Thanks, the recent guidance or rule requiring bidirectional protection, is that a publicly accessible document?
Maybe worth a read.
Thanks. It doesn't mention MCBs at all, is that because MCBs are inherently bidirectional, or is it because no bidirectional MCBs are made?
I admit to having some trouble visualise the "direction" of AC current, given it's going backwards and forwards anyway. I guess it's the relationship with voltage .. in phase = forwards, 180 out phase = reverse. Or something.
I would really like the installer to fit an MCB, or lower sensitivity RCBO as Solaredge clearly warn that nuisance trips are to be expected with a 30mA RCBO. But of course it needs to be compliant.
I think most, if not all, MCBs are bidirectional. As I understand it, the problem with some unidirectional RCDs is they have electronics that can be damaged should the load side remain energised after tripping. This would be the case with solar, hence the need for bidirectional devices. Whereas MCBs are mechanical devices that are connected in the line conductor only, they shouldn't be damaged should either side remain energised when open AFAIK.
Unidirectional devices will have markings to indicate that, while bidirectional devices will not. Useful info here:
Feature about bidirectional devices in this month's Professional Electrician. It seems that the required mod is to add an extra switch contact into the device to disconnect the electronics completely when it trips.
As #19
One solution adopted by manufacturers to address this issue is to include a switching contact linked to the contacts in the line and neutral conductors, as shown in Fig 5. With this arrangement, when the device trips the supply to the amplifier and solenoid is also disconnected.
Thanks everyone. I guess the reason for needing two pole disconnection is that in the case of a fault you can't trust the inverter not to interfere with N as well.
Anyway the installers are coming next Tuesday to replace the RCBO, even if I'm not sure what they'll replace it with.
aesmith
Aberdeenshire
RCD Needed on Circuit to Solar Inverter (UK)?
DIY Electrical Advice
aesmith,
aesmith,