Our solar inverter is connected to a dedicated circuit from an RCBO in a CU in our garage. The RCBO was chosen, supplied and installed by the solar installers. The cable runs up from the CU in plastic trunking, goes through a concrete block wall to the next room, then is clipped to the wall and along a purlin at ceiling height before dropping down to the inverter in plastic conduit.

Since installation last May the RCBO has tripped twice for no apparent reason. I haven't had any feedback yet from the installer, but after the first trip they said there was no indication of any fault with the inverter. I have suggested that they replace the RCBO just for elimination.

However looking at information from the manufacturer, Solaredge, it seems they're not particularly keen on an external RCD. They recommend that if one if fitted it should be 100mA or 300mA, and there's a comment that where "local codes" require a 30mA RCD then there may be nuisance trips.

But before exploring that further I'd just like to confirm the current requirements. From what I've described, does it sound as if RCD protection is required on that particular circuit cable run?

Thanks,
 
It possibly doesnt need one.

Under the regs, a circuit would need RCD protection if any of the following were true

Supplies sockets not exceeding 32A
Passes through, or serves a room containing a bath or shower
Any circuit with luminaires (lights)
Is buried in a wall less than 50mm deep*

*This is the one that covers basically everything in a newbuild house... but if you say the cable is surface run, even in trunking...... it may not be required.


The installers, however, may have their own procedures that EVERYTHING must be RCD protected whether it requires it or not.
 
Hi,

Our solar inverter is connected to a dedicated circuit from an RCBO in a CU in our garage. The RCBO was chosen, supplied and installed by the solar installers. The cable runs up from the CU in plastic trunking, goes through a concrete block wall to the next room, then is clipped to the wall and along a purlin at ceiling height before dropping down to the inverter in plastic conduit.

Since installation last May the RCBO has tripped twice for no apparent reason. I haven't had any feedback yet from the installer, but after the first trip they said there was no indication of any fault with the inverter. I have suggested that they replace the RCBO just for elimination.

However looking at information from the manufacturer, Solaredge, it seems they're not particularly keen on an external RCD. They recommend that if one if fitted it should be 100mA or 300mA, and there's a comment that where "local codes" require a 30mA RCD then there may be nuisance trips.

But before exploring that further I'd just like to confirm the current requirements. From what I've described, does it sound as if RCD protection is required on that particular circuit cable run?

Thanks,
What's the model number ?

Most inverters will have an internal rcd
These inverters by construction cannot feed DC fault current into the installation, as required by IEC 60364-7-
712:2002.

I would change the rcd to a type A 100ma, as suggested by the manufacturer.
 
What's the model number ?

Most inverters will have an internal rcd
These inverters by construction cannot feed DC fault current into the installation, as required by IEC 60364-7-
712:2002.

I would change the rcd to a type A 100ma, as suggested by the manufacturer.
Thanks. It's a Solaredge "Home Hub" inverter model SE6000H-RWBMNBF54.

If the Wiring Regulations say an RCD is needed, doesn't that mean it needs to be 30mA?
 
Type of earthing (ie:TT) could require (RCD) Residual Current Device to meet disconnection times,also buried in walls,passing though bathroom or supplying standard sockets will require one.little spark explains this better above
 
Thanks. Earthing is TNS. The circuit runs entirely within a detached outbuildings, from the garage into an adjoining utility room where the solar gear is installed. Does passing through a wall perpendicular to the surface count as buried in the wall?
 
Thanks. Earthing is TNS. The circuit runs entirely within a detached outbuildings, from the garage into an adjoining utility room where the solar gear is installed. Does passing through a wall perpendicular to the surface count as buried in the wall?
No, it doesn't. (It's a fair question though!) You're all good
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

aesmith

DIY
-
Joined
Location
Aberdeenshire

Thread Information

Title
RCD Needed on Circuit to Solar Inverter (UK)?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
aesmith,
Last reply from
aesmith,
Replies
9
Views
145

Advert

Back
Top