gamblor6

hi guys. long time lurker part time poster here, job has been done. tn c s earth, outside lights, roughly 30 meters from db. metallic light fittings. should these have there own spike or are they ok with the earth of the armour? im thinkink they are small caravans if you know what i mean.
 
Never really heard or thought of a light fitting being compared to a caravan myself.


Sent from my iPhone using Tapatalk
 
STOP HIJACKING THREADS!!! you have posted 3x now on the same subject 2x as a thread and one as a post!
 
What's the problem with taking the earth from the armour? What Zs have you obtained?
 
zs was within limits. im just wondering why we cant transport tn c s to a caravan, if we look at bulkhead light fittings as small caravans, far fetched i know, is it within bs 7671 to take tn c s to them? or should i have spiked them? its a sticky subject i know. just wondering what you guys think.
 
The ESQCR regulations 2002 preclude a combined neutral and protective conductor being connected to any metalwork in a caravan, this is primarily because under certain fault conditions, a potential can develop between the conductive parts connected to the PME earth terminal and the general mass of earth.

I wouldn't be concerned with bulkhead fittings however lighting columns set in the ground are a whole threads' worth of debate!
 
as iq says widdler. these are not set in the ground they are fixed to the wall. im not really that bothered but know that way when jobs just bug you, lol.
 
as iq says widdler. these are not set in the ground they are fixed to the wall. im not really that bothered but know that way when jobs just bug you, lol.

I would consider them to not be subject to an alternative earth potential if they are fixed to the wall, and so the armouring and RCD should suffice.
 
zs was within limits. im just wondering why we cant transport tn c s to a caravan, if we look at bulkhead light fittings as small caravans, far fetched i know, is it within bs 7671 to take tn c s to them? or should i have spiked them? its a sticky subject i know. just wondering what you guys think.

Are we discussing the use of bulkheads as caravans for extremely small persons here?:confused:
 
ooompah loomphs pehaps lol someone needs to look out for them. i just cant see why the big (caravan) and the small (bulkhead light fitting) make a diferance for me the problem of 25 v or so potential diff still exists aqaaarrrrggghhhh im going to eat my own head.
 
ooompah loomphs pehaps lol someone needs to look out for them. i just cant see why the big (caravan) and the small (bulkhead light fitting) make a diferance for me the problem of 25 v or so potential diff still exists aqaaarrrrggghhhh im going to eat my own head.

The difference is that under an open circuit neutral fault condition, you wouldn't be inside a bulkhead light fitting (well I wouldn't be).
 
why would you have to be inside? surely the potential dif still exists between the fitting and the general mass of earth. an electricians hands may be inside the fitting also.
 
why would you have to be inside? surely the potential dif still exists between the fitting and the general mass of earth. an electricians hands may be inside the fitting also.

In which case it should be isolated and Definetly no potential than :P
 
Gamblor think your putting too much thought into it, if bulkheads are suitable for outdoor use etc etc just go ahead and wire it in armour, personally I'd use 3core rather then 2 core and using the armour as an earth I'd still earth the armour but I'd have a seperate core for a direct earth. Also you can use the new earthing nuts that save u from drilling the accessories and messing with the ip integrity of the fitting!
 
cheers gaulty jobs been done, just used the armour as earth. the only times the armour is too small to be used as earth is summit like 250 mm and 300 mm lines. agreed im thinkin too much. still think the problems are the same tho, where in scotland are you gaulty?
 
the pme thing is just for main bonding.you dont need main bonding to a light fitting just cpc earthing.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
transporting earths again
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
24

Thread Tags

Advert

Thread statistics

Created
gamblor6,
Last reply from
nick611,
Replies
24
Views
2,603

Advert

Back
Top