If you looked at a job of a garage or similar, in which was supplied via a 30ma RCD protected circuit from the house and the customer wanted to add a few more sockets, add another flourescent and a couple of bulk head lights on the outside, would you leave the supply as is or convert it so RCD protection is local within the buildeing itself?

Lets not bring up, is it a TT earthing, is their extraneous parts etc etc. Keep it simple. The supply cable calcs all allow it to be fed via a 32 A MCB.

Just wondering as i've priced and they are but 2 other sparkes have quoted to do it different to me.:confused:
 
as long as loading , volt drop, and compliance with BS7671 are achieved, ok to leave as is.
 
I would change it so the RCD was local to the garage , pain in the butt having to go back to the house when the RCD trips especially if its blowing a hoolie and chucking it down like it is today
 
I would change it so the RCD was local to the garage , pain in the butt having to go back to the house when the RCD trips especially if its blowing a hoolie and chucking it down like it is today
but that's no fun!!!
 
If the garage is supplied by a T&E, i would leave the RCD in house.

If SWA, then yes, RCD local.
 
Leave it as it is, in the house and explain to the customer where and how to reset the rcd. After all they won't be in the garage sleeping or in complete darkness stumbling to find the cu. But if its a TT system I would........;);)
 
If the garage is supplied by a T&E, i would leave the RCD in house.

If SWA, then yes, RCD local.

Yes its SWA

quote for both and explain difference

Problem here is that the price is going into the joiners whos doing some roofwork and studding out for them. Knowing him, he'll probably stick my highest price in and tell the customer that he's priced for the cheaper option.
 