Quick Question - Max Permitted Zs Values

Discuss Quick Question - Max Permitted Zs Values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

byrnie_2004

On an Installation Cert in the 'Max Permitted Zs' column should i put the tabulated values in the regs or should i put the corrected values(x0.8 rule of thumb)????
My guess would be corrected values as that would be max zs at ambient temperature at the time of test?
Cheers peeps,

Dan:cool:
 
As I understand it, you are expected to put in the uncorrected tabulated values from BS7671.
If thes are NICEIC or Napit forms, I believe you are also expected to put in the uncorrected measured values.
Bit weird, but that's the scheme providers for you.
 
general opinion is to enter the brb ( uncorrected ) figures on the test sheet, but the readings you get should be below the corrected figures. very rare to see cables reaching max. temp. of 70 deg. anyway
 
but if it's a TT system with RCD protection, you can enter 1667.
 

Reply to Quick Question - Max Permitted Zs Values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock