VoltzElectrical
the point i was making was that the CPC on a flex may not intercept the fault at all......yes ok..this can happen with T&E ....but less likely due to the structure of this type of cable....
How would that work??
There is nothing wrong with using flex to wire a whole house, other than the prohibitive costs. As for the reg being quoted re. fixed wiring.... what does that mean? Just follow the normal routes. All that need s to be considered as far as the regs go, are current carrying capacity, heat resistance, and disconnection times with due accord to heating under fault conditions (adiabatic equation). Other than that, it id down to cost/ convenience factors. bootlace ferrules? over-egging the omelette IMHO.