Always a tough one to call for the following reasons... If you have an electrically separate piece of copper pipe somewhere near the plastic incomer, plus bits of copper piping in the rest of the installation AND you test between this short piece (plus all your other pipes) and the MET and you get in excess of 23k ohms, then you could confidently say (as others have pointed out) that this pipework is not going to introduce a potential.
However, a year down the line, the homeowner has a boiler fitted and the conscientious plumber arranges for a sparky to main bond the incoming gas pipe. Said sparky slaps his 10mm cable in and goes home happy.
Unfortunately, now we have some continuity between the pipework in the system, but it's not perfect and we get some resistance. Now, if someone were to get a shock (for whatever reason), the first question would be "Why wasn't the main water incomer bonded?"
I realise that I have painted a bit of a far-fetched scenario, but I think this is a why most electricians would say "If it's not all plastic then put a 10mm main bond in". That way, if it anything gets altered then you have covered yourself.
However, a year down the line, the homeowner has a boiler fitted and the conscientious plumber arranges for a sparky to main bond the incoming gas pipe. Said sparky slaps his 10mm cable in and goes home happy.
Unfortunately, now we have some continuity between the pipework in the system, but it's not perfect and we get some resistance. Now, if someone were to get a shock (for whatever reason), the first question would be "Why wasn't the main water incomer bonded?"
I realise that I have painted a bit of a far-fetched scenario, but I think this is a why most electricians would say "If it's not all plastic then put a 10mm main bond in". That way, if it anything gets altered then you have covered yourself.