I have my 302 Practical exam (testing) on Wednesday. I just wanted to know if I am right in what I'm doing.

1. First you would do the Testing of the Protective conductors. Using the R2 method (Long Lead)
2. Then you would do the R1+R2 Tests of all your circuits. Connecting Live and Earth at the board and test at the load.
3. Ring Final test. Connecting Incoming Live with outgoing CPC and vice versa
4. Insulation Resistance Test. 500V down all cable turning on all switches
5. Polarity. Do a visual Inspection and see if it all works correctly.

Live test:

1. ZE test. Test between Main Protective Earth and the incoming Live.
2. PFC test. The same time as the ZE test.
3. ZS test. Testing between the cables at the load
4. RCD testing. Test at 1/2x 1x 5x the rated current, at 0degrees and 180degrees


Is this correct or is there something wrong. Or is there anything that I need to know??????


I would really appreciate any help

Thanks
 
I have my 302 Practical exam (testing) on Wednesday. I just wanted to know if I am right in what I'm doing.

1. First you would do the Testing of the Protective conductors. Using the R2 method (Long Lead)
YES (Bonding Conductors)
2. Then you would do the R1+R2 Tests of all your circuits. Connecting Live and Earth at the board and test at the load.
YES
3. Ring Final test. Connecting Incoming Live with outgoing CPC and vice versa
NO END to END TEST FIRST
4. Insulation Resistance Test. 500V down all cable turning on all switches
YES
5. Polarity. Do a visual Inspection and see if it all works correctly.
?? Polarity R1+R2 Dead test then at sockets Martindale type tester

Live test:

1. ZE test. Test between Main Protective Earth and the incoming Live.
YES
2. PFC test. The same time as the ZE test.
PEFC with earth connected PSCC Line & Neutral
3. Depends if you are going to use R1 +R2 +ZE to give you Zs
ZS test. Testing between the cables at the load
4. RCD testing. Test at 1/2x 1x 5x the rated current, at 0degrees and 180degrees
YES DONT forget mechanical test (Press the yellow button)

Hope this helps
T&E


Is this correct or is there something wrong. Or is there anything that I need to know??????


I would really appreciate any help

Thanks[/QUOTE]
 
Youre pretty much on track there mate.
Just add on functional tests at end to make sure all equipment works.
Job done and good luck.
 
Dead test only need R1+R2 or R2
More to do on ring final test r1 rn r2 & cross connect neutrals
pfc should be done to neutral & phase to phase on a TPN system if the tester is capable of phase to phase if not use rule of thumb (double the highest of pefc of pfc)
 
Just a couple of points:
Take each earth out of the board for R1+R2 to avoid parallel paths,
operate the switches as you're doing R1+R2 which will check polarity,
It might be worth looking up ring final testing in the onsite guide - you need to test end to end before figure of 8.
PFC is the highest of PEFC (3 lead) and PSCC (2 lead).
The last RCD test is to check operation of the test button, then finally test functionality by switching everything on.
 
Did mine a few months ago and we were NOT allowed to use Martindale type socket testers. Knowing end to end R of L,N and CPC the only way we were allowed to test was by crossing say L & N at cu (then L & CPC), totalling R and dividing by 4 and then testing R at each individual socket. It should be very close to the predicted results. The purpose of doing it this way is to identify any spurs as well as confirming polarity
 
For a Ze test don't forget to isolate the installation - prove it is isolated, then disconnect the earthing conductor then carry out test (at least that is what I was taught).
 
and if its an initial verefication then R1 R2 and Zs at ALL POINTS of the installation..IR can be conducted globally.....
 
Most important thing to do first is SAFE ISOLATION, then prove its dead with gs38 approved voltage indicators and a proven unit. DO NOT give the key of your pad lock/device to your tutor or you will fail!!!


Good luck

Jay
 
Most important thing to do first is SAFE ISOLATION, then prove its dead with gs38 approved voltage indicators and a proven unit. DO NOT give the key of your pad lock/device to your tutor or you will fail!!!


Good luck

Jay
proving unit...or a known source of supply..such as the incoming side of a DP isolator....
 
DO NOT give the key of your pad lock/device to your tutor or you will fail!!!
When I did my level 3 you had to pretend to put the key in your pocket, then leave it on the side. The examiner assured us it wasn't a 'trick' - they've had people who have messed up the safe isolation and run out of the workshop in distress with the key still in their pocket, and the padlock has had to be removed using the 'master key' which has cost the college a new padlock.
 
When I did my level 3 you had to pretend to put the key in your pocket, then leave it on the side. The examiner assured us it wasn't a 'trick' - they've had people who have messed up the safe isolation and run out of the workshop in distress with the key still in their pocket, and the padlock has had to be removed using the 'master key' which has cost the college a new padlock.
well they may accept that at college Adam ....but you wont get away with that one on the 2391.....if that warning label isn`t on that lock that you will/should have put on that iso and that key dont go in your pocket....pack your bags...you`v failed....
 
Last edited by a moderator:
At college our tutor actually asked us for the key. He made up some excuse like, "incase the fire alarm gos off, I need it so it wont get lost". If you gave him it, you failed. Sneaky bugger!!!

Jay
 

OFFICIAL SPONSORS

Back
Top