martinh89
As you quite rightly calculate that 4 x 600w would equate to over 10 amps so putting that on the end of a radial with sockets would NOT be the way to go.
Looks like you need 1 x radial for the sockets and 1 x radial for the lights - both 2.5mm and 16a breakers (or you could go to 20A depening on the cable routing).
And as new circuits its notifiable and does the house have RCD's and bonding in place?
cheers mate , theres no radial circuit for the lights , its just 1 radial circuit for the socket outlests for plug in lights , the cable run is pretty straight forward , straight up from the downstaires C/U to the loft in trunking.
He does have a socket on the staires directly under the loft on a ring main, could i branch off that by any chance without installing a new circuit ?????