I can't see the image as I'm on my phone but sometimes there is enough slack to wedge a screwdriver between the carrier and base and hold it apart with the seal intact. Other wise I've had to cut the tag, you can buy seals and tags online and re crimp them afterwards, but they won't have the markings on then from the DNO.
 
remove the red cable from the henley, job done

NO
Turn off the main switch on the consumer unit first = no load
Then remove both the red and the black cables from the Henleys. Remember Neutral is also a live conductor.

Looking at the Henleys, you still have to cut the DNO seals on there (why do they do that?)

To LEX

If you involve the DNO then they may require a BS7671 cert or other certificate of safety/compliance before reconnecting.

I'm hoping that you have a full set of calibrated test equipment so you can check your new consumer unit?
I am also hoping that you have (or will) notify the local authority before starting work, or are you a registered electrician?.
 
nowt wrong with cutting the seals on the henleys, they're not DNO's .
 
Aren't they sealed just to stop the uninitiated/hard of thinking from poking around in them?
 
To LEX

If you involve the DNO then they may require a BS7671 cert or other certificate of safety/compliance before reconnecting.

I'm hoping that you have a full set of calibrated test equipment so you can check your new consumer unit?
I am also hoping that you have (or will) notify the local authority before starting work, or are you a registered electrician?.

I have a fluke for testing. I'm registered with JIB but haven't told the local authority anything just yet. I've spoken to the DNO, they are coming out to fit a proper isolator so this issue won't come up again.
 
Do these new meters not have the built in isolator, I can see a small black hole top right but can't tell what it is, if there's a slotted screw in there a ninety degree turn isolates it.
Personally I would just take the cables out of the henleys.
 
Do these new meters not have the built in isolator, I can see a small black hole top right but can't tell what it is, if there's a slotted screw in there a ninety degree turn isolates it.
Personally I would just take the cables out of the henleys.
well....from what i remember there was a hoo ha over this....the DNO didn`t like the idea of built-in iso`s as they stood to lose money.....shameful really.....elf n sayfti anyone?...
 
I have a fluke for testing. I'm registered with JIB but haven't told the local authority anything just yet. I've spoken to the DNO, they are coming out to fit a proper isolator so this issue won't come up again.

Hmm, what sort of Fluke meter will that be then.
Does it have Insulation Resistance, low ohm and RCD testing facilities?

also

Does JIB allow you to self certify and notify installations in accordance with Part P? I wasn't aware of that little loophole....
 
Hmm, what sort of Fluke meter will that be then.
Does it have Insulation Resistance, low ohm and RCD testing facilities?

also

Does JIB allow you to self certify and notify installations in accordance with Part P? I wasn't aware of that little loophole....

Yes its all singing all dancing, didn't realise I'd signed up for the Spanish inquisition.
Doing a favour for a mate not commissioning big Ben!
 