I tend to test at a socket/light fitting, then if anything 'odd' shows up I test it at the board compare the results and go from there.
As Murdoch pointed out though, a slow RCD can frequently be brought back to spec with a few presses of the manual test button.
I had a Legrand 63amp 3 phase RCD fail a couple of weeks ago.
When it was first turned on it went bang, even with all the MCB's turned off, when I tried it again it shut down the whole system including the digital meter. After about 30mins, system cooled down and came back up on line with 230 volts present at each phase. RCD was badly scorched on the sides so ordered a new one and replaced. Cost of new one Euros 283.60 and thats trade price here in France.
i had a legrand 63amp 3 phase rcd fail a couple of weeks ago.
When it was first turned on it went bang, even with all the mcb's turned off, when i tried it again it shut down the whole system including the digital meter. After about 30mins, system cooled down and came back up on line with 230 volts present at each phase. Rcd was badly scorched on the sides so ordered a new one and replaced. Cost of new one euros 283.60 and thats trade price here in france.
£200+ ???
J
But if the rcd is requiring the manual button pumping a few times then obviously the rcd inside is breaking and needs replacing, there is no guarantee that in 1 yrs time when joe public needs the rcd to trip under fault that it will trip
It's not breaking, the mechanism is sticking. That's why the should be (and a label to that effect is put on the CU) manually tripped annually. No one bothers though, consequently they stick. Working the mechanism a few times usually frees them off.
That's the arse about face way of doing things!! lol!! Your RCD tester, is good for testing RCDs of all descriptions, not the circuit(s) it's protecting....
Plugging in the RCD doesn't 'test' the circuit E54 that hopefully would have been done with the dead tests and the Zs test, you are simply using the conducters to test the RCD,if as some people seem to think its a good thing to limit 'Live' testing..what's safer ? Plug it in or probes ?
J
Plugging in the RCD doesn't 'test' the circuit E54 that hopefully would have been done with the dead tests and the Zs test, you are simply using the conductors to test the RCD,if as some people seem to think its a good thing to limit 'Live' testing..what's safer ? Plug it in or probes ?
J
Adds to the resistance of the provided leads though doesn't it as well as measuring through any noise or whatever on the neutral and CPC!! I wonder why all the manufacturers of RCD devices ALL recommend testing at the load side of the device itself??
Which are exactly the circumstances under which the RCD is required to work if a fault occurs. So to my mind the testing at that point is a far more accurate description of the RCD's 'real' operation. As I said, if all is fine there then that's that, if not then test at the RCD and go from there based on your findings.
I give up!!!
Deservices,
Engineer54,