so its an EICR is it?....if so then you cant sample on this circuit.....check all points served.....including any joint boxes.....
while your at it...make a note of any stuff like neons etc that will throw up silly IR readings later on.....unless you just test live to earth that is....
 
Don't forget that this is an existing installation, so the fact that r2 is lower than the r1 is understandable and most probably due to existing parallel earth paths. The r1 reading equates to approx 40-45 metres, so check if this is right.
although the rn reading is high and does suggest loose connections.
 
Don't forget that this is an existing installation, so the fact that r2 is lower than the r1 is understandable and most probably due to existing parallel earth paths. The r1 reading equates to approx 40-45 metres, so check if this is right.
although the rn reading is high and does suggest loose connections.

He's not put the r2 figure, just r1 and rn.

also shouldn't be any parallel paths on an end to end cpc test.
 
No problem mate.
Incedenly, existing installations even though the loads are disconnected, the cpcs,s are still continuous and can often find parallel earth paths within the installation.
 