dave30

hello im changing a consumer unit from old style bs3036 semi enclosed fuses the fuse ratting are as follows 5 15 30 15 30 30 amp


if i was replacing with bs 60898 mcb would i use the following sizes 6 16 32 16 32 32 amp


and will this be ok taking into account the size of the conductors of each circuit and the max carrying capacities being

1.5 mm csa for 5 amp

2.5 mm csa for 15 amp

and 2.5 mm csa for the 30 amp two of witch are radial and one is a ring


all instaled in in method 102


thanks again for all your help
 
i would advise you dont, the old and new sizes do not match up and can cause a very dangerous situation if you altered
 
In an ideal world you will.

But in reality when changing an old BS3036 board you may find the fuses are of the incorrect rating in the first place.
 
Depends on what the circuit is supplying?
as you have said check to see if they are in fact a continuous ring and not two radials other they will need to be on 16 amp.
Is there only 1 lighting cicuit?

- - - Updated - - -

Depends on what the circuit is supplying?
as you have said check to see if they are in fact a continuous ring and not two radials other they will need to be on 16 amp.
Is there only 1 lighting cicuit?
 
hello im changing a consumer unit from old style bs3036 semi enclosed fuses the fuse ratting are as follows 5 15 30 15 30 30 amp


if i was replacing with bs 60898 mcb would i use the following sizes 6 16 32 16 32 32 amp


and will this be ok taking into account the size of the conductors of each circuit and the max carrying capacities being

1.5 mm csa for 5 amp

2.5 mm csa for 15 amp

and 2.5 mm csa for the 30 amp two of witch are radial and one is a ring


all instaled in in method 102


thanks again for all your help





think that the two 16 amp fuses are lighting
 
sorry to sound insulting dave but this is really simple stuff, if you don't know how to, don't change the board mate and can you notify it, are you a member of a scam, seriously this is really really simple , sorry fella but I had to say it.
 
My advise would be to refers to bs7671 for cable sizes chart, you dont want to be installing too larger size mcb's for the size of cable. dont put the radial circuits on a 32A mcb unless the cable is 4mm or above, 2.5mm cant handle 32amps (according to bs7671)
 
hello im changing a consumer unit from old style bs3036 semi enclosed fuses the fuse ratting are as follows 5 15 30 15 30 30 amp


if i was replacing with bs 60898 mcb would i use the following sizes 6 16 32 16 32 32 amp


and will this be ok taking into account the size of the conductors of each circuit and the max carrying capacities being

1.5 mm csa for 5 amp

2.5 mm csa for 15 amp

and 2.5 mm csa for the 30 amp two of witch are radial and one is a ring Cant have a 2.5mm radial on a 32a OCPD...20a max


all instaled in in method 102


thanks again for all your help

Given the rather basic nature of your question I'd have to ask if you are able to carry out the required testing of the existing circuits. You will need to carry out as a minimum IR tests to ensure RCD's wont trip...and Zs tests to ensure your new OCPD's meet disconnection times.....As well as RCD tests and effectiveness of earthing.
If you cant carry out these tests you'll be on here after the CU swap, asking why the RCD's wont stay in.

- - - Updated - - -
 
i have just completed my 2392 inspection and testing my 17th edition wiring regs and my part p building regs but have no one to ask for help and clarafication


have all my own tools and have a reasonable grasp of what im doin just need help


i imagine its possible to change these fuses to mcb and of course i will clarify all the requirements with the reg books witch i have

#just looking for pointers and some help

- - - Updated - - -

i have just completed my 2392 inspection and testing my 17th edition wiring regs and my part p building regs but have no one to ask for help and clarafication


have all my own tools and have a reasonable grasp of what im doin just need help


i imagine its possible to change these fuses to mcb and of course i will clarify all the requirements with the reg books witch i have

#just looking for pointers and some help
 
Thing is dave, look sorry to say this buddy really, but a second year apprentice could answer your questions on this board change, I like you and don't want to insult you honestly, but this is really really simple and you shouldn't need clarification.
 
i will visit the house tomorrow and confirm the csa of all the cables and the propose of all the individual circuits


think i have the csa mixed up

and then reply again thanks for your help
 