can you not fit a stand alone DCD/MCB in an enclosure ( about 7" x 5" ) adjacent to the meter cupboard, for the shower as a temporary measure? i'd use a 63A/30mA RCD with a 40A MCB up to 9.5kW.
 
can you not fit a stand alone DCD/MCB in an enclosure ( about 7" x 5" ) adjacent to the meter cupboard, for the shower as a temporary measure? i'd use a 63A/30mA RCD with a 40A MCB up to 9.5kW.

What would be the suitability like with just a 63A/30mA RCD enclosure...sited next to the CU (with cupboard made bigger)?....effectively RCD wired between the CU 40A and the 45A DP pull switch, as a temporary measure...instead of a dedicated RCD/MCB unit, with new tails.

I have been through the forums and there are very mixed views on this subject amongst electricians...mainly regarding regs, compliance and where an RCD can be fitted on the circuit.

cheers
 
Last edited by a moderator:
Nothing wrong with that mate

Would definitely be cheaper and easier if you don't want too much disruption
 
Instead of faffing around looking for unusual ways of providing Rcd protection whilst not prepared to allow the space for the work to be done

It's not apparent where the tails are fed from but I will assume an external meter cabinet
If you don't want necessary alteration to the fuse board cupboard,it has been known on many properties for an Rcd for the whole installation be fitted in that meter cabinet
 
How far do the meter tails run, or where are they run from?

If you have access and it's possible you could put an upfront RCD on them and in the same enclosure add a RCBO for the sockets/ shower to account for discrimination. Or just start the shower circuit there. Still much preferable to just increase the size of the cupboard
 
Des is right, I could have done the job 10 times over by now, stop faffing about LMAO

I have already altered the stud wall and made access far large enough for a new CU.

It is all down to the cost unfortunately, as had to give up full time work due to personal circumstances.

Ideally and eventually, a new CU will be installed...but I want to make sure at least the shower circuit will be as safe as possible until then, which has obviously taken time to gather helpful responses.


So it's unusual for a Shower RCD unit to be installed next to the CU?..
 
quote
So it's unusual for a Shower RCD unit to be installed next to the CU?..


Bobby you have so many comments about so many different alternatives and whether the cupboard is staying ,going to getting bigger,whether the cons unit is being changed or is staying or being altered whether the Rcd is going in the attic, being mounted by the new or is it old board,henley blocks,meter cabinets,Rcbo yes/no

I think.you as well as myself are confused
Shall we all start again
:tt1:
 
quote
So it's unusual for a Shower RCD unit to be installed next to the CU?..


Bobby you have so many comments about so many different alternatives and whether the cupboard is staying ,going to getting bigger,whether the cons unit is being changed or is staying or being altered whether the Rcd is going in the attic, being mounted by the new or is it old board,henley blocks,meter cabinets,Rcbo yes/no

I think.you as well as myself are confused
Shall we all start again
:tt1:

ha, I think that is the most useful comment of all! I have caused all the confusion...I know mate.

i should have just bit the bullet, and hacked the cupboard out first... Cheers
 
All sorted now. The shower circuit is now RCD protected, with an RCD Enclosure next to the CU...just got a bit more faffing about to do between building a new cupboard over it!

Cheers to everyone for your helpful advice.
 