can you not fit a stand alone DCD/MCB in an enclosure ( about 7" x 5" ) adjacent to the meter cupboard, for the shower as a temporary measure? i'd use a 63A/30mA RCD with a 40A MCB up to 9.5kW.
Nothing wrong with that mate
Would definitely be cheaper and easier if you don't want too much disruption
Des is right, I could have done the job 10 times over by now, stop faffing about LMAO
So it's unusual for a Shower RCD unit to be installed next to the CU?..
No not at all Fella![]()
quote
So it's unusual for a Shower RCD unit to be installed next to the CU?..
Bobby you have so many comments about so many different alternatives and whether the cupboard is staying ,going to getting bigger,whether the cons unit is being changed or is staying or being altered whether the Rcd is going in the attic, being mounted by the new or is it old board,henley blocks,meter cabinets,Rcbo yes/no
I think.you as well as myself are confused
Shall we all start again:tt1:
shame you didn`t join a few months ago....Ok, cheers...I realise I am tarting about a bit!!!