Although you should always leave the CPC connected to the MET when doing an IR test

According to the latest edition of GN3, the requirement to have the CPC connected to the means of earthing while doing IR testing was introduced in the 17th edn, 2008. Para 612.3.1 of 7671:2008 amd1 refers.

Of course, if you're just fault finding, as opposed to certifying, you can do what you like within reason.
 
According to the latest edition of GN3, the requirement to have the CPC connected to the means of earthing while doing IR testing was introduced in the 17th edn, 2008. Para 612.3.1 of 7671:2008 amd1 refers.

Of course, if you're just fault finding, as opposed to certifying, you can do what you like within reason.


Indeed, don't shoot the messenger. Just because I quote a reg, or recommendation, it doesn't mean I agree with it :)
 
Sorry, wasn't having a pop at you

I know you weren't mate. That said, I DO get used to being moaned at by customers and other trades when I quote a reg. My favourite saying at the moment is "I don't make the rules, I just have to follow them." This is usually followed when talking to a builder or plumber with them saying "But my usual electrician never bothers..." :)
 